[Bldg-sim] Claiming refrigerated casework savings for a LEED project
Jim Dirkes
jim at buildingperformanceteam.com
Thu Jan 23 05:07:06 PST 2014
Another good insight. Thank you!
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: Rosenberg, Michael I [mailto:Michael.Rosenberg at pnnl.gov]
Sent: Wednesday, January 22, 2014 9:46 PM
To: Jim Dirkes
Cc: EnergyPlus_Support at yahoogroups.com; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Claiming refrigerated casework savings for a LEED project
Jim,
The 2013 version of ASHRAE Standard 90.1 added requirements for refrigerated casework. I suggest you identify where your project exceeds those requirements and make the case to USGBC that what is in 90.1 should be the baseline. Good luck.
__________________________
Michael Rosenberg, CEM, LEED AP
Senior Research Scientist
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street<x-apple-data-detectors://0/0>
Eugene, OR 97405<x-apple-data-detectors://0/0>
(541) 844-1960<tel:(541)%20844-1960>
michael.rosenberg at pnnl.gov<mailto:michael.rosenberg at pnl.gov>
www.pnnl.gov<http://www.pnl.gov/>
On Jan 22, 2014, at 17:33, "Jim Dirkes" <jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>> wrote:
Dear Forum,
I am modeling a supermarket which has made effort to install refrigerated casework that is more efficient than "normal" in three ways:
* Casework lighting is LED instead of fluorescent
* Evaporator fans use ECM motors and are demonstrably more efficient
* The compressors have higher COP
I did not realize that claiming savings from a "process" load also requires substantiation of the Baseline energy for the process load via comparison to several similar facilities or a published paper. I wish I knew that months ago!
We have data from three other supermarkets owned by the same company, but these other examples are not identical. So far, all I can say is that:
a) Manufacturer literature claims that LEDs used in their casework use ~ 65% less energy than fluorescent lights
b) ECM fans use about 35% less energy in a manufacturer power comparison table
c) The COP is better (I do not have detailed data yet)
This strikes me as a fairly weak argument, so I am asking you for suggestions or published data to strengthen the argument.
p.s., My last alternative is to ignore the process energy savings and make it the same for both models. I think the savings are substantial, however, and would rather find a way to claim them!
<image003.png>
"Attack me ... rather than the path I follow and which I point to anyone who asks me where I think it lies. If I know the way home and am walking along it drunkenly, is it any less the right way because I am staggering side to side?" Leo Tolstoy
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140123/cce3ae22/attachment-0002.htm>
More information about the Bldg-sim
mailing list