Michelle,
In case you didn't get an answer to your question yesterday afternoon.
Sounds like you are looking at the system types in Section 11 (ECB method),
but for LEED projects, the appendix G modeling protocol must be used
(Performance Rating Method). As for the H&V only warehouse, you should look
at Addendum dn to 90.1-2007 which establishes H&V baseline systems and
provides some guidance. Alternatively, you can look in 90.1-2010 Appendix G.
Hope this helps.
Cam Fitzgerald
Energy Opportunities/a 7group company