Thu May 8 09:17:00 PDT 2014
compared to an air conditioner that has an economizer, is this correct?
There would not be any additional compressor savings, is this correct?
Thanks,
Jon McHugh
=20
-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Michael
Rosenberg
Sent: Thursday, December 21, 2006 1:03 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Modeling buildings with natural ventilation
forAppendix G
Marcus,
I am on the ASHRAE 90.1 ECB subcommittee. I do not think at this point
that we are working on any additional methodology to credit natural
ventilation. Addendum AG already changed the following:
In the proposed building.
HVAC Fan Schedules. Schedules for HVAC fans that provide outdoor air for
ventilation shall run continuously whenever spaces are occupied and
shall be cycled on and off to meet heating and cooling loads during
unoccupied hours.=20
This implies that HVAC fans that are only meeting thermal load may cycle
on and off, and was meant to allow fan credit for natural ventilation
system (as simple as operable windows). The proposed building still
calls for cooling as a requirement, but the thought is, that if model
simulates natural ventilation and the cooling load is met that way, the
fan and cooling coil will not operate to meet load and the design will
be credited. The problem is that most LEED models are done using DOE2,
which has severe limitations when it comes to modeling natural
ventilation. It is my understanding that other programs do a better job
of this. =20
The subcommittee also thought that an exceptional calculation method
might be used if the natural ventilation simulation was be done in a
stand alone program and then an appropriate infiltration schedule was
input into a program like DOE2, reducing the use of mechanical cooling.
Mike
Michael Rosenberg
Oregon Department of Energy
625 Marion St. N.E.
Salem, OR 97301-3742
Phone : (503) 373-7809
Fax: (503) 373-7806
>>> "Marcus Sheffer" <sheffer at sevengroup.com> 12/21/06 11:58AM >>>
Mike,
=20
The exception calculation method you describe is absolutely correct.
=20
Obtaining savings for natural ventilation within LEED however is another
story. I am one of the certification reviewers and also vice-chair of
the EA TAG. My understanding is that to date the USGBC has not allowed
natural ventilation to fully count under EAc1 even if submitted as an
exceptional calculation method. The TAG is awaiting the work of the
90.1 subcommittee you mention to develop a uniform methodology.
=20
Perhaps your submission will be the one to set the precedent. Thanks to
all for helping to blaze the trail.=20
=20
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, <mailto:sheffer at sevengroup.com> sheffer at sevengroup.com=20
www.sevengroup.com=20
=20
_____ =20
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Mike
Tillou
Sent: Thursday, December 21, 2006 2:03 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Modeling buildings with natural ventilation for
Appendix G
=20
Not yet...I have a project with natural ventilation using this method
that will be submitted for final review in Feb-Mar 2007. =20
=20
MMT
Michael Tillou, PE
ETC Group, Inc - Energy Engineering for a Sustainable Future
Ph:413-458-9870=20
-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Peter
Alspach
Sent: Tuesday, December 19, 2006 1:34 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Modeling buildings with natural ventilation for
Appendix G
Mike,
=20
Have you succeeded in getting a naturally ventilated building through
the USGBC with this method?
=20
If so, I am sure all would be glad to hear it.
=20
Peter
=20
_____ =20
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Mike
Tillou
Sent: Tuesday, December 19, 2006 7:18 AM
To: bldg-sim at gard.com
Subject: [bldg-sim] Modeling buildings with natural ventilation for
Appendix G
Ramana,
=20
The ASHRAE 90.1 ECB sub-committee is working on a methodology for
simulating natural ventilation within the framework of Appendix G but I
don't think its finished yet. In the meantime here is what I would
recommend.
=20
Appendix G / 90.1 ECB allows you to use an exception calculation method
to simulate hybrid systems or unique efficiency measures to demonstrate
above-standard performance. I think this would certainly apply in your
case. =20
=20
Here's what I have done on projects requiring an exception calculation
method. =20
1. Establish your energy cost budget and your design energy case
following the Appendix G guidelines. =20
2. Create a second model using the Design Energy Case as the baseline
and make the necessary modifications to simulate radiant heating / no
cooling via natural ventilation. =20
3. Report the energy savings from your exception calculation as a line
item at the end of your LEED EA-1 summary table (similar to how
renewable energy is reported).=20
4. Include a seperate summary table for the exception calculation
showing the energy end-use breakdown and how you arrived at the cost
savings.=20
Show
both the baseline and proposed energy use. =20
5. Make sure the savings are reasonable and prudent for the system you
are proposing. =20
6. Document any changes to the model especially changes to schedules
that were necessary to properly simulate your system.=20
7. Make it easy for someone to review your assumptions and the
methodology you used to estimate the savings
=20
I hope this helps. Good luck.
=20
Mike
=20
Michael Tillou, PE
ETC Group, Inc - Energy Engineering for a Sustainable Future
Ph:413-458-9870=20
-----Original Message-----
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Ramana
Koti
Sent: Monday, December 18, 2006 4:53 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Modeling buildings with natural ventilation for
Appendix G
Dear all,
Is ignoring natural ventilation in both proposed and baseline designs an
accepted/fair way of modeling based on Appendix G (ASHRAE 90.1-2004)?
Part of the proposed design has (radiant heating + natural ventilation)
with no cooling which was modeled as a radiant slab, no cooling, natural
ventilation ignored.=20
But the Baseline HVAC system based on Appendix G is System 5: Packaged
VAV w/Reheat. (Natural ventilation can be modeled based on Air Change
method or Sherman Grimsrud method though I do not know how to do it).
I cannot decide how to make the baseline and proposed comparable with
respect to Natural Ventilation (in a manner acceptable to LEED review),
suggestions will be appreciated.
Thanks,
Ramana Koti, Sustainable Building Analyst LEED AP
ELEMENTS | a division of berkebile nelson immenschuh mcdowell architects
106 W. 14th Street Suite 200
Kansas City, Missouri 64105
p 816.783.1635 f 816.783.1501
www.bnim.com| elements.bnim.com
=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
____________________________________________________________
Electronic mail messages entering and leaving Arup business systems are
scanned for acceptability of content and viruses
=20
=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM=20
=20
=20
=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM=20
=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=
=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=
=3D=3D=3D=3D
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=
=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=3D=
=3D=3D=3D=3D
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list