Craig, thanks for the reply.
I should have been clearer on my objective. The intent is not to
condition the space. I am calculating the stack effect potential for
an underground parking garage. I want to know if a chimney can help
reduce the fan consumption, if yes by how much.
As part of the calculation, I need to know the temperature profile in
the space, hence I also need to know the heat gains from the cars.
The building is in the tropics. The fresh air for CO concentration
control as per 62.1 has already made the temperature go up to 35
degC. I have not included the heat gain from the cars. Higher
temperature will be good for stack effect, but too high is not good
for comfort.
I will check out Airtest data. Any further information along this
line would be appreciated.
Thanks,
Ery
On Sun, 11 May 2014, Craig Gann wrote:
> Conditioning of garage temperature is secondary consideration to exhaust
> of CO. Std 62.1 requires 0.75 cfm/sf of exhaust for a parking garage.
> Depending on climate you may get by with conditioning using only exhaust
> (outside) air and CO sensors to stage or modulate exhaust fans as traffic
> volume (CO level) fluctuates. There is no typical usage schedule for
> parking garages. Offices will differ greatly from shopping malls or
> condos. Do a web search for a company called "Airtest" which makes CO
> sensors and has research data available about controlling parking garage
> exhaust fans using CO.
>
> Regards,
>
> Craig J. Gann, P.E.
>
> On 5/11/2014 5:11 PM, Ery Mailing-List wrote:
>
> Folks,
> Is there an example on how to model underground parking garage:
> 1. heat gains from (different models of) car
> 2. entrance/exit as a function of time of day
> Thanks,
> Ery
>