[Bldg-sim] Tolerance for unmet load hours
    Annie Marston 
    A.Marston at baumann-us.com
       
    Wed May 28 12:04:34 PDT 2014
    
    
  
Oh I definitely agree about gaming the system, it is very easy with this. I also agree about finding the root cause of your unmet load hours that is very important. It would just be nice to have some guidance as it can take a long time to get your unmet load hours down if you are using the tolerance of 0.2°C and make very little difference to the energy savings between the two buildings. I just felt the fairest way to do it was to follow a software that had the tolerance set that was also used commonly to submit to LEED.
ANNIE MARSTON, Ph.D., LEED AP, BEMP
Senior Consultant, Head of Building Performance
[cid:image009.jpg at 01CF2284.8C44F2B0]
1424 K Street NW | Suite 500 | Washington, D.C. 20005
main +1 202 608 1334 | direct +1 202 407 9395
email a.marston at baumann-us.com<mailto:a.marston at baumann-us.com>
www.baumann-us.com<http://www.baumann-us.com/>
[LinkedIn]<http://www.linkedin.com/company/ebert-&-baumann-consulting-engineers-inc->
From: Jim Dirkes [mailto:jim at buildingperformanceteam.com]
Sent: Wednesday, May 28, 2014 2:48 PM
To: Annie Marston; Michael Tillou; 'King-Scott, Celia'; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Tolerance for unmet load hours
Beware - don't get seduced.  This setting is a "gaming" temptation for some software.  Bigger tolerance means less unmet load hours and can become a simple way to get within the ASHRAE limits. Better to figure out why you have the unmet hours in the first place!
That said, I had a project a while back with too many unmet load hours and figured out why they were occurring.  Without going into details, the model was correct and the unmet load hours were also correct.  As it happened, I had left the tolerance at the default value of .2C.  That was unrealistically low, so I changed it to .5C (.9F) and unmet load hours were within ASHRAE tolerances.
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Annie Marston
Sent: Wednesday, May 28, 2014 1:49 PM
To: Michael Tillou; 'King-Scott, Celia'; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Tolerance for unmet load hours
I had the very same question and couldn't find the answer, but I was told that Trane Trace uses 1.1°F / 0.83°C. So we use that as a default when modelling for LEED. But the only thing I could find was as Michael Tillou says, it must be the same for baseline and design case.
I am interested to know what other people have experienced.
Thanks!
Annie
ANNIE MARSTON, Ph.D., LEED AP, BEMP
Senior Consultant, Head of Building Performance
[cid:image009.jpg at 01CF2284.8C44F2B0]
1424 K Street NW | Suite 500 | Washington, D.C. 20005
main +1 202 608 1334 | direct +1 202 407 9395
email a.marston at baumann-us.com<mailto:a.marston at baumann-us.com>
www.baumann-us.com<http://www.baumann-us.com/>
[LinkedIn]<http://www.linkedin.com/company/ebert-&-baumann-consulting-engineers-inc->
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Michael Tillou
Sent: Wednesday, May 28, 2014 1:44 PM
To: 'King-Scott, Celia'; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Tolerance for unmet load hours
Hi Celia,
ASHRAE 90.1 Appendix G would simply require that the tolerance be the same in both the baseline and proposed design energy models.
Cheers,
Mike
Michael Tillou, PE, LEED AP BD+C, ASHRAE BEMP
Associate
Atelier Ten
Environmental Design Consultants + Lighting Designers
45 East 20th Street, 4th Floor
New York NY 10003
T +1 (212) 254 4500 x208
F +1 (212) 254 1259
michael.tillou at atelierten.com<mailto:michael.tillou at atelierten.com>
www.atelierten.com<http://www.atelierten.com>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of King-Scott, Celia
Sent: Wednesday, May 28, 2014 1:38 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Tolerance for unmet load hours
Does anyone know what the ASHRAE limitation on the tolerance (in F) for unmet load hours is. Design Builder/EnergyPlus appears to have this tolerance for the heating and cooling setpoint. It is defined as the maximum difference from the heating setpoint when the reporting the time setpoints are not met (for both heating and cooling). If the zone temperature is below the heating/cooling setpoint by more than this value an unmet load hour will be reported.
There is a similar input in eQUEST called the 'Cool control range' and 'Heat control range'.
If you increase the value of this tolerance you will get smaller number of unmet load hours. I was told once that ASHRAE has a limit on what this tolerance is however I am unable to locate it.
Any help would be greatly appreciated.
Thank you!
Best regards
for KEMA Services Inc., USA
Celia King-Scott PE, BEMP, LEED® AP BD+C
Senior Engineer, Sustainable Buildings & Communities
E-mail celia.king-scott at dnvgl.com<mailto:celia.king-scott at dnvgl.com>
Mobile +16193097441 begin_of_the_skype_highlighting  |  Direct +16196880960 begin_of_the_skype_highlighting x 75120
www.dnvgl.com<http://www.dnvgl.com/>  |  LinkedIn<http://www.linkedin.com/company/dnvgl>
DNV KEMA is now DNV GL
[DNV GL]<http://www.dnvgl.com/>
DNV and GL have merged to form DNV GL
We are now the world's largest ship and offshore classification society, the leading technical advisor to the global oil and gas industry, and a leading expert for the energy value chain including renewables and energy efficiency. We've also taken a position as one of the top three certification bodies in the world. Read more here: www.dnvgl.com/merger<http://www.dnvgl.com/merger>.
This message may contain confidential or private information. If you are not the addressee, please return the message to its sender and delete it from your files. Please consider the environment before printing this email.
sender and delete it from your files. Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140528/e52f5878/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3362 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140528/e52f5878/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 813 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140528/e52f5878/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.gif
Type: image/gif
Size: 2815 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140528/e52f5878/attachment.gif>
    
    
More information about the Bldg-sim
mailing list