Hi, everyone.
I think that we are talking about W/m^2 per 100 lux. This is the measure for maximum lighting power density (LPD) in some
European countries regulations like from Portugal or Spain.
An example: if the maintained average illuminance in a room is 300 lux and the maximum LPD per 100 lux is 2,5 W/m^2
then the maximum LPD for that room is 7,5 W/m^2. 
If you want a similar measure with US standard it will be something like W/ft^2 per 10 fc or other illuminance quantity.
Best Regards.
António Manuel Almeida
aalmeida at isec.pt
INESC Coimbra
Portugal
  ----- Original Message ----- 
  From: Christian Stalberg 
  To: bldg-sim at lists.onebuilding.org 
  Sent: Wednesday, May 28, 2014 11:21 AM
  Subject: [Bldg-sim] question regarding lighting efficiency/gains units ofmeasurement
  In Europe one sees W/m2-100 lux as a measure of lighting related gains or lighting efficiency. What is the equivalent here in the states? I suspect it is a messy conversion.
   
  Thank you in advance.
   
  Regards,
  _
  Christian Stalberg
  Natural Intelligence, LLC
  http://naturalintelligence.us
  Tel. 415.531.4610
   
------------------------------------------------------------------------------
  _______________________________________________
  Bldg-sim mailing list
  http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
  To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
---
Este email está livre de vírus e malware porque a proteção avast! Antivirus está ativa.
http://www.avast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140529/8cd79fa6/attachment.htm>
    
    
More information about the Bldg-sim
mailing list