[Bldg-sim] 90.1-2010 Appendix G heat source question
    Nicholas Blanton 
    nicholas.blanton at arup.com
       
    Fri Nov 14 13:27:41 PST 2014
    
    
  
Chris - Here is some insight from a comparable situation, although the system types are different:
Three C&S office buildings that I've modeled have energy recovery ventilators (ERV-located on the roof) that use gas for heating. The terminal units throughout the building contain electric heating coils. The gas heating coil in the ERV is intended to be used in the following scenarios:
1)      The energy wheel goes down
2)      To keep the ERV discharge air temperature above 32F (heat air so the discharge is a minimum of 40F for freeze protection purposes)
For simulation purposes, I have found that, given the high efficiencies of the energy wheel and given the TMY3 weather data, the gas energy consumption is either not engaged at all or is sufficiently small compared to the electric energy consumption (<10% of total heating energy consumption).
For this reason, I have been able to justify going with System 4 or System 8. The energy savings of the proposed building when compared to the gas/electric hybrid baseline building is much less than the all-electric baseline building.
Regards,
Nicholas E Blanton LEED AP BD+C
Mechanical Engineer
Arup
1120 Connecticut Avenue NW  Suite 1110  Washington DC 20036  USA
t +1 202 729 8220    d +1 202 729 8241
m +1 505 228 4154
www.arup.com<http://www.arup.com/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Friday, November 14, 2014 4:01 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] 90.1-2010 Appendix G heat source question
The proposed design has 9 floors and has heat recovery chillers, air-to-water heat pumps and natural gas boilers for the heating plant.  Based on Table G3.1.1A, I selected System 5.  Based on G3.1.3.2, I selected electric boiler as the predominate heat source is electric.
Based on G3.1.1 exception b.  I have some spaces that require a single zone system.  As the building has Fossil/Electric Hybrid heating, I select System 3 - PSZ-AC.  My question is: should the heat source of these systems be gas furnace as per Table G3.1.1A or should I select electric resistance as the predominate heat source is electric?
Thanks for any insights!
Christopher Jones, P.Eng.
Halsall Associates
Tel: 416.644.4226 * Toll Free: 1.888.425.7255 x 527 *  www.halsall.com<http://www.halsall.com/>
Vancouver * Calgary * Sudbury  * Burlington * Toronto * Ottawa
Best Workplaces in Canada, Seven Consecutive Years: 2007 - 2013
___________________________
A Parsons Brinckerhoff Company
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20141114/741d6489/attachment.htm>
    
    
More information about the Bldg-sim
mailing list