[Bldg-sim] 90.1-2010 Appendix G heat source question
Cheney
chenyu73 at gmail.com
Fri Nov 14 14:09:43 PST 2014
Hi Chris,
1. >5 floors should be system 7 with hybrid heating source?
2. The selection of system for those special spaces in the building is
based on the heating source for the main building (Please see user's manual
p. G-28 for details). That's why you pick up system 3 which should be
fossil fuel furnace. You can not use predominate heating source here.
*Best Regards, *
*Cheney*
Connect with me and view my *http://lnkd.in/bqQf52i*
<http://lnkd.in/bqQf52i>
On Fri, Nov 14, 2014 at 1:01 PM, Jones, Christopher <cjones at halsall.com>
wrote:
> The proposed design has 9 floors and has heat recovery chillers,
> air-to-water heat pumps and natural gas boilers for the heating plant.
> Based on Table G3.1.1A, I selected System 5. Based on G3.1.3.2, I selected
> electric boiler as the predominate heat source is electric.
>
>
>
> Based on G3.1.1 exception b. I have some spaces that require a single
> zone system. As the building has Fossil/Electric Hybrid heating, I select
> System 3 – PSZ-AC. My question is: should the heat source of these systems
> be gas furnace as per Table G3.1.1A or should I select electric resistance
> as the predominate heat source is electric?
>
>
>
> Thanks for any insights!
>
>
>
>
>
> *Christopher Jones**,* P.Eng.
> *Halsall Associates*
> Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527 • www.halsall.com
> Vancouver • Calgary • Sudbury • Burlington • Toronto • Ottawa
> *Best Workplaces in Canada, Seven Consecutive Years: 2007 - 2013*
>
> *___________________________*
>
> *A Parsons Brinckerhoff Company*
>
>
>
>
>
> ______________________________________________________________________
> NOTICE: This communication and any attachments ("this message") may
> contain confidential information for the sole use of the intended
> recipient(s). Any unauthorized use, disclosure, viewing, copying,
> alteration, dissemination or distribution of, or reliance on this message
> is strictly prohibited. If you have received this message in error, or you
> are not an authorized recipient, please notify the sender immediately by
> replying to this message, delete this message and all copies from your
> e-mail system and destroy any printed copies.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20141114/5a7e242b/attachment.htm>
More information about the Bldg-sim
mailing list