Sambhav,
What do you mean when you say that the conduction gains have increased?  
Do you mean that there's less conduction heat flow entering the 
building, or more ?  If it's the former, that makes a lot of sense, 
since the shading is cutting off solar gain on the wall/window, thus 
lowering its surface temperature (or more exactly, sol-air temperature) 
and reducing heat flow into the building.  If it's the latter, that 
would be problematic, since I don't see how reducing solar gain would 
increase conduction heat flow entering the building.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
http://www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 11/24/2014 7:00 AM, Andrew Corney wrote:
> Hi Sambhav,
>
> Yeah - I'd agree with Cory - you probably have a higher glazing 
> surface temperature with the unshaded model and I wouldn't be 
> surprised if that is part of the conduction equation, meaning you are 
> less likely to gain heat through conduction if the glazing is in full sun.
>
> cheers,
>
> Andrew
>
> On Mon, Nov 24, 2014 at 2:55 PM, Duggin, Cory <Cory.Duggin at tlc-eng.com 
> <mailto:Cory.Duggin at tlc-eng.com>> wrote:
>
>     The VE doesn’t model thermal bridging, so that isn’t it.  What
>     climate is your building in?  What percentage glazing are the east
>     and west walls? Are you losing heat through the envelope or
>     gaining it?  It could have to do with the shades blocking more sun
>     from heating up the outside of the envelope on those walls, which
>     then changes the delta T and resulting conduction gain.
>
>     *Cory Duggin, EI, LEED AP BD+C *
>
>     /Associate/Energy Engineer/
>
>     *TLC Engineering for Architecture *
>
>     direct:
>
>     	
>
>     615-346-1939 <tel:615-346-1939>
>
>     *From:*Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org
>     <mailto:bldg-sim-bounces at lists.onebuilding.org>] *On Behalf Of
>     *Sambhav Tiwari
>     *Sent:* Monday, November 24, 2014 2:21 AM
>     *To:* Attiq
>     *Cc:* bldg-sim
>     *Subject:* Re: [Bldg-sim] Building Heat Gains
>
>     Hi All,
>
>               Thanks for the reply this analysis was done in ies ve
>     and the external conduction gains are increasing with shading
>     while solar gains are reducing
>
>     i am sending the snapsort of the building with shading in east and
>     west
>
>     Regards
>
>     Sambhav
>
>     On Sat, Nov 22, 2014 at 9:46 PM, Attiq <aur at bepc.biz
>     <mailto:aur at bepc.biz>> wrote:
>
>     The shades are attached to the building exterior and there is no
>     thermal break between the shades and the exterior walls. The
>     shades act as fins conducting heat to the outside.
>
>     Attiq
>
>     Sent from my iPhone
>
>
>     > On Nov 22, 2014, at 7:15 AM, Sambhav Tiwari
>     <tiwari.sambhav at gmail.com <mailto:tiwari.sambhav at gmail.com>> wrote:
>     >
>     > Dear All,
>     >                I am analyzing a rectangular building with each
>     and west facades structured glazed and forming longer sides of
>     rectangle  and i shaded these facades with louvers (shading device)
>     >
>     > I compared the annual heat gains of two case1 building with no
>     shading case 2 building with shading(louvers) what i found was
>     there is considerable reduction in annual solar gains in building
>     but the annual external conduction gains in building have
>     increased after shading i am unable to understand this.
>     >
>     > Any one who can share his ideas on this.
>     >
>     >
>     > Warm Regards
>     > Sambhav Tiwari
>
>
>     _______________________________________________
>     Bldg-sim mailing list
>     http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>     To unsubscribe from this mailing list send  a blank message to
>     BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>     <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> -- 
> Andrew Corney
> PE M.CIBSE M.ASHRAE
> Product Director
> Sefaira - Software for Energy Efficient Building Design
> Mobile: +44 (0)7887 059 722
> Office: +44 (0)2037 147 619
> Skype: andrew.corney.sefaira
>
>
>         Sefaira - Sustainability. Performance. Design.
>         /
>         /
>         /For company contact and registration information, please
>         visit: http://www.sefaira.com/info/contact/
>
>         /Interested in performance based design? Subscribe here
>         <http://www.sefaira.com/subscribe-from-email/> to our
>         bi-weekly newsletter./
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20141126/7aea39c5/attachment.htm>
    
    
More information about the Bldg-sim
mailing list