[Bldg-sim] Precipitation value in stat extension file.
    Dru.Crawley at bentley.com 
    Dru.Crawley at bentley.com
       
    Fri Sep  5 14:03:46 PDT 2014
    
    
  
The 2013 ASHRAE Handbook-Fundamentals includes monthly precipitation data for each station:  average monthly, standard deviation, and minimum/maximum monthly precipitation (see image of summary table from chapter 14).
The data in the 2013 Fundamentals come from a number of sources, some of which include hourly data:
GHCN. 2011. GHCN monthly. National Climatic Data Center, National Oceanic and Atmospheric Administration, Asheville, NC. http://www.ncdc.noaa.gov/ghcnm/
GPCC. 2011. Global Precipitation Climatology Centre data.
ftp://ftp-anon.dwd.de/pub/data/gpcc/html/gpcc_normals_download.html
FAO. 2011. Climate impact on agriculture. Food and Agriculture Organization of the United Nations, Rome. http://geonetwork3.fao.org/climpag/agroclimdb_en.php
NASA. 2008. Surface meteorology and solar energy. Atmospheric Science Data Center, National Aeronautics and Space Administration, Washington, D.C. http://eosweb.larc.nasa.gov/sse
VASClimO. 2011. ftp://ftp-anon.dwd.de/pub/data/gpcc/html/vasclimo_download.htm
[cid:image001.png at 01CFC92A.6372EFC0]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Mayank Bhatnagar
Sent: Friday, August 29, 2014 11:13 AM
To: Joe Huang
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Precipitation value in stat extension file.
Thank you for your valuable suggestions.
Thank you joe, I am looking on source files for precipitation/ rainfall data.
I hope, I will get your suggestions in future also.
Regards,
Mayank
On Aug 28, 2014 6:26 AM, "Joe Huang" <yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>> wrote:
Sounds liked you're referring to Precipitable Water, which has no relationship to the actual liquid precipitation falling on the ground. PW is reported in the TMY2/3 weather files, mainly because it's used along with a few other arcane variables (aerosol optical depth, albedo) in modeling solar radiation. These are all echoed in the EPW, which content-wise is 99% identical to the TMY2/3s, but I can't think of any reason why any of these variables would be used in EnergyPlus.
Another reason I'm doubtful of your explanation is that PW is typically reported in depth (0.1 cm in the TMYs) and not pressure.
Sent from my IPad
Joe Huang
On Aug 27, 2014, at 3:59 PM, "Collinge, William Overton" <woc6 at pitt.edu<mailto:woc6 at pitt.edu>> wrote:
The variable in kPa is probably showing the total column water vapor. kPa water vapor divided by atmospheric pressure (101.3 kPa or thereabouts at sea level) would be an aggregate measure of absolute humidity i.e. an average over the vertical profile at some specific location.
Not sure what it is subsequently used for in E+?
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Michael J Witte
Sent: Wednesday, August 27, 2014 3:52 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Precipitation value in stat extension file.
Not sure what this section of the EnergyPlus stat file is reporting (will get this fixed or clarified)
 - Monthly Indicators for Precipitation/Moisture (kPa)
                    Jan    Feb    Mar    Apr    May    Jun    Jul    Aug    Sep    Oct    Nov    Dec
                    1.4      1.6      1.8      1.8      2.3      2.6      2.9      2.8      2.7      2.2      1.8      1.3
But if you keep searching for "precipitation" you'll find what I think you're looking for
 - Monthly Statistics for Liquid Precipitation mm
                    Jan    Feb    Mar    Apr    May    Jun    Jul    Aug    Sep    Oct    Nov    Dec
       Total       117      43       97       0        0        83       0        0        0        0        0        31
     Max Hourly    36       13       14       0        0        17       0        0        0        0        0        6
That said, I would echo Joe's comments about using this information with caution.  Some data sources do not contain actual precip amounts but only a flag for raining or not raining.  The weather processor will fill in approximate precip amounts in that case.
Mike
On 8/27/2014 12:50 PM, Joe Huang wrote:
Mayank,
You're right.  kPa is a unit of pressure, so somehow the header units you're using have been misaligned.  I won't comment on what you see in the EPW, but if you look at the source weather file, which probably uses a TMY3 or TMY2/IWEC format (the only ones I know that contain precipitation data), there are two columns for liquid precipitation, one for depth in mm followed by one for duration in hr.
Having said that, from my investigations in creating the IWEC2 weather files I've concluded that this way of reporting the liquid precipitation can lead to missing or double counting the amount of precipitation. The reason is that in the actual weather station reports, there may be multiple reports in one record, e.g.,
   100mm over the past 1 hour and 500mm over the past 24 hours
as well as reports that overlap in time, e.g.,
   200mm over the past 4 hours
followed several hours later by
   400mm over the past 24 hours
I've attached the brief-up about liquid precipitation from the IWEC2 final report with more details.
The other thing to consider is that if you're using a "typical year" weather file, the liquid precipitation on that file are a random selection and may not represent long-range averages.  Depending on your level of interest, it's best to go back to the source historical weather files such as those available at NCDC:  www.ncdc.noaa/oa/climate/isd/<http://www.ncdc.noaa/oa/climate/isd/>
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 8/27/2014 8:59 AM, Mayank Bhatnagar wrote:
Dear All,
I am doing some analysis on weather file in which I need precipitation value in mm or  inches. However, when I look on stat extension file, there is monthly precipitation value in kPa. As I know 'kPa' is a unit of pressure. Please let me know if anyone has  conversion factor for monthly precipitation value from kPa to mm(inches).
The epw extension file has hourly precipitation value in mm. However, all the weather files do not have hourly precipitation values.
I'll be grateful if anyone can guide me on this. :)
Regards,
Mayank
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140905/8ea9bfff/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 130005 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140905/8ea9bfff/attachment.png>
    
    
More information about the Bldg-sim
mailing list