[Bldg-sim] Variation in incident solar radiation on east and west surface of a building in different simulation tool
Jim Dirkes
jim at buildingperformanceteam.com
Sat Sep 27 00:01:56 PDT 2014
Congratulations, Sherlock; you have solved the mystery very handily!
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Joe Huang
Sent: Friday, September 26, 2014 8:39 PM
To: Jeff Haberl
Cc: bldg-sim at lists.onebuilding.org; equest-users at lists.onebuilding.org
Subject: Re: [Bldg-sim] Variation in incident solar radiation on east and west surface of a building in different simulation tool
I've been corresponding with Mayank offline and have determined that the cause for the difference is due entirely to the 30 minute difference between the GMT 5.50 time zone for India, and the GMT 5.0 integer time zone input into eQUEST.
I'm summarizing the e-mail exchange with Mayank below for those who may be curious as to the cause and solution for this discrepancy in solar radiation on different orientations.
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 9/26/2014 6:23 AM, Mayank Bhatnagar wrote:
Dear Joe,
Thanks for your response.
We took your recommendations and have been able to resolve the problems. Results for east and west facade are consistent for Eplus and eQuest post the longitude correction.I have attached these files for your reference as well.
[cid:image002.jpg at 01CFD9FF.649C3380][cid:image004.jpg at 01CFD9FF.649C3380]
Regards,
Mayank
On Fri, Sep 26, 2014 at 7:14 AM, Joe Huang <yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>> wrote:
Mayank,
I suspect that this discrepancy in the peaks is an artifact of the eQUEST/DOE-2 limitation of accepting only integer time-zones.
One way to adjust for this is to move the longitude of the building site by 7.5 degrees, i.e., if you input the time zone as 5, then subtract 7.5 degrees from the building location, and if you input the time zone as 6, then add 7.5 degrees to the building location.
I was going to experiment with that, but then thought it would save some of my time if you could send me your eQUEST (*.inp) and EnergyPlus (*.idf) input files. That would also clarify to me which variables you're pulling out as the solar radiation terms.
Thanks.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 11:59 AM, Mayank Bhatnagar wrote:
Dear Joe,
I am using the same weather file for both energy plus and eQuest. As eQuest uses BIN format I converted the same epw format file using eQ_wthProc tool (EPW to BIN converter). I have attached a spreadsheet (New Delhi_ISHRAE_2014EPW.xlsx) that compares Total global Horizontal radiation and direct normal radiation for EPW file (by converting it into CSV format) and eQuest hourly outputs (as it reads BIN file). Since both the global horizontal and direct normal radiations are identical, conversion from epw to bin seems correct. Additionally, as you know, eQuest doesn't take diffused radiation from the weather file, it calculates itself.
Since I am using the same source file for both eQuest and Eplus simulations I would expect similar trend in solar radiation data for both East and West facades. However, for Delhi I found variation in solar radiation output for east and west facade. I have attached results spreadsheet (eQUest and energy plus_Miami and Delhi_v1.xlsx) for your reference.
Interestingly, when I performed a similar analysis for "Miami epw and bin file", I got fairly consistent results (refer graph below, the results are for June 6 to June 9)
(plots deleted)
On 9/24/2014 8:18 AM, Jeff Haberl wrote:
FYI:
You also didn't say that you're using the EPW weather file in EQUEST, only that EQUEST is using .BIN format (or binary). Is EQUEST using TMY2 or TMY3?
Jeff
8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=) 8=?
Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......jhaberl at tamu.edu<mailto:........jhaberl at tamu.edu>
Professor........................................................................Office Ph: 979-845-6507
Department of Architecture............................................Lab Ph:979-845-6065
Energy Systems Laboratory...........................................FAX: 979-862-2457
Texas A&M University...................................................77843-3581
College Station, Texas, USA, 77843..............................URL:www.esl.tamu.edu
8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=) 8=0
________________________________
From: Bldg-sim [bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] on behalf of Peter Simmonds [psimmonds11 at gmail.com<mailto:psimmonds11 at gmail.com>]
Sent: Wednesday, September 24, 2014 10:15 AM
To: Mayank Bhatnagar
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Fwd: Variation in incident solar radiation on east and west surface of a building in different simulation tool
Try checking the date and time set on the programs. One could be using summertime hours ?
Peter Simmonds, Ph.D., ASHRAE Fellow and DL
Mobile US: +1-310-383-9911
Mobile HKG: +852-9845-4902
Mobile UK: +44 7711 926317
On Sep 24, 2014, at 8:06 AM, Mayank Bhatnagar <mayank.23aug at gmail.com<mailto:mayank.23aug at gmail.com>> wrote:
Dear Dru,
Yes, I am using the same weather file for all simulation tools. eQuest used bin format, which I have already checked with weather file (epw format). The bin file only have total horizontal radiation and Normal direct radiation, the diffuse radiation is being calculated by eQuest itself (as per Joe huang's mail: previously asked for a query on eQuest users). TRNSYS and E+ used epw format.
The variation are found in radiation falling on east and west surface of the building.
Regards,
Mayank
On Wed, Sep 24, 2014 at 8:23 PM, Dru Crawley <dbcrawley at gmail.com<mailto:dbcrawley at gmail.com>> wrote:
Are you using the same hourly weather data in eQuest, TRNSYS and EnergyPlus? The radiation can vary significantly.
On Wed, Sep 24, 2014 at 7:42 AM, Mayank Bhatnagar <mayank.23aug at gmail.com<mailto:mayank.23aug at gmail.com>> wrote:
Dear All,
I am doing envelope analysis of a rectangular building in eQuest. The building have identical parameters for all perimeter zones. The simulation is being done for New Delhi climate zone. The results shows that the total solar heat gain through glazing is more in east zone compare to west zone. In the result of that the total load and energy consumption in east zone is higher than in west zone.
To verify the results, I analyzed the total horizontal and beam radiation incident on east and west facade. Here, the issue was started. In the eQuest, there always high incident solar radiation in east surface compare to west surface. However, the incident solar radiation on east and west surface in energy plus and TRNSYS have different trend from the eQuest. Here I am attaching graph showing variation of incident solar radiation in east and west facade with energy plus and TRNSYS.
Any guidance, suggestions will be appreciated.
1. Variation in eQuest and TRNSYS. (Blue and green is for eQuest and; Magenta and brown for TRNSYS)
<image.png>
2. eQuest and Energy Plus
<image.png>
Regards,
Mayank Bhatnagar
Energy Analyst
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140927/d502713b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 18431 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140927/d502713b/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 18466 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140927/d502713b/attachment-0001.jpg>
More information about the Bldg-sim
mailing list