[Bldg-sim] The calculated ground temperature exceeds -100 C
    Jianhua Huang 
    jh.eco.cas at gmail.com
       
    Wed Feb  4 10:58:47 PST 2015
    
    
  
Hi Mike:
Thanks for the information. I just checked the idf file, and it looks that
the evapotranspiration is set to FALSE by default. (I found two
evapotranspiration parameters in the file, and they are both set to FALSE)
  GroundHeatTransfer:Slab:BoundConds,
    FALSE,                   !- EVTR: Is surface evapotranspiration modeled
    TRUE,                    !- FIXBC: is the lower boundary at a fixed
temperature
    10,                      !- TDEEPin {C}
    FALSE;                   !- USRHflag: Is the ground surface h specified
by the user?
  GroundHeatTransfer:Basement:SurfaceProps,
    0.16,                    !- ALBEDO: Surface albedo for No snow
conditions
    0.4,                     !- ALBEDO: Surface albedo for snow conditions
    0.94,                    !- EPSLN: Surface emissivity No Snow
    0.86,                    !- EPSLN: Surface emissivity with Snow
    6,                       !- VEGHT: Surface roughness No snow conditions
{cm}
    0.25,                    !- VEGHT: Surface roughness Snow conditions
{cm}
    False;                   !- PET: Flag, Potential evapotranspiration on?
I also tried to update the EnergyPlus to V8.1 and V8.2. Unfortunately, none
of them work, and I still get the same errors. 
Any other idea what happened? Thanks for any suggestion!
Sincerely,
Jianhua
-----Original Message-----
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
Michael J Witte
Sent: Wednesday, February 04, 2015 8:36 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] The calculated ground temperature exceeds -100 C
The EnergyPlus Slab preprocessor fails with some weather files when
Evapotranspiration= TRUE.  A fix was made to get around this in v8.1.  
With v7.2, if you change Evapotranspiration to FALSE, it should run
successfully.  EnergyPlus is now at v8.2.
Mike