Wet-bulb is not generally measured in weather stations, but can be derived from other
measured climatic variables, such as dry-bulb temperature, dew-point temperature, and
atmospheric pressure. Unfortunately, the derivation requires several equations and
trial-and-error iteration (see Chapter 1 of the ASHRAE Handbook of Fundamentals). If you
don't relish writing a script or program to do this, you can look at the unpacked DOE-2
format (*.FMT or *.FMTM) of the weather file, which does contain the calculated wet-bulb
temperatures in the first data column (see attached sample snippet). However, you will
need a utility Fortran program wthfmt2.f or wthfmt3.f to convert the packed (*.BIN or
*.BINM) DOE-2 file to a humanly -readable text *.FMT or *.FMTM file.
E-mail me for details.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 2/9/2015 12:33 PM, RobertWichert wrote:
> These weather files are great, thanks for the info, but I am trying to get wet bulb
> temperature too, and they do not seem to give wet bulb temperatures.
>
> Any ideas on that, perhaps?
>
>
> --
> Robert P. Wichert P.Eng. LEED AP
> CEPE CEA HERS I/II BPI BA
> +1 916 966 9060
> FAX +1 916 966 9068
>
>
> ========================================
> On 1/30/2015 9:10 PM, Joe Huang wrote:
>> White Box Technologies (WBT), in collaboration with the National Renewable Energy
>> Laboratory (NREL), has revised the TMY3 weather files to correct inconsistencies in
>> units for illuminances, improve the reporting of Liquid Precipitation, replace all
>> missing records with interpolated or filled values (chiefly for visibility, ceiling
>> height, aerosol optical depth, and albedo), and add a new variable for Present Weather.
>>
>> Since their release in 2005, the TMY3 weather files covering 1,020 locations in the US
>> and dependencies has become the standard set of weather files for use in computer
>> simulations of solar energy conversion systems and buildings. The intent of this
>> revision is not to redo the fundamental analysis, but correct some known errors and
>> make modest improvements in the reporting of subsidiary climate variables.
>>
>> The only impact from these corrections and changes are for daylighting simulations that
>> use the illuminance values, and for building simulations that use the liquid
>> precipitation to model green roofs or moisture transport through the building envelope.
>> The added Present Weather variable is not directly used in any simulation program, but
>> allows the DOE-2 BINM files to have correct IRAIN and ISNOW flags, although these two
>> variables are not being used in DOE-2. Filling in missing data for Visibility, Ceiling
>> Height, etc., should have no impact on the use of the TMY3s, but improves their overall
>> record-keeping.
>>
>> The revised TMY3 files in their native CSV format have been provided back to NREL and
>> are available here: http://rredc.nrel.gov/solar/old_data/nsrdb/1991-2005/tmy3
>>
>> The revised TMY3 files in EPW and BINM formats are available for free download on the
>> White Box Technologies web site at http://weather.whiteboxtechnologies.com/wd-TMY3 or
>> by selecting File Type as "TMY3" at http:/weather.whiteboxtechnologies.com/search to
>> search using GoogleEarth. The zip file names are unchanged, but the underlying EPW and
>> DDY files will have the *TYA designation to distinguish them from the previous TMY3
>> versions.
>>
>> For a more detailed description and full documentation of the revision, please see the
>> attached memorandum.
>>
>> Joe
>> --
>> Joe Huang
>> White Box Technologies, Inc.
>> 346 Rheem Blvd., Suite 205A
>> Moraga CA 94556
>> yjhuang at whiteboxtechnologies.com
>> http://weather.whiteboxtechnologies.com for simulation-ready weather data
>> (o) (925)388-0265
>> (c) (510)928-2683
>> "building energy simulations at your fingertips"
>>
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message toBLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150209/804539ed/attachment.htm>
More information about the Bldg-sim
mailing list