[Bldg-sim] LEED v4 ligthing devices
    David GARCIA SANCHEZ 
    dgarciasanchez at greenaffair.com
       
    Tue Feb 24 02:42:47 PST 2015
    
    
  
Thanks for your answer,
I didn’t saw the definition of « luminaire » in the standard before, since it state that it consist of a lamp or lamps together I suppose that at the moment  that the reduction of 30% is achieved and my group of lamps is less than 3 600 ft2 I’m ok ☺
[cid:image004.png at 01D05026.BE3EA420]
Thanks again for your answer!
Mr. Koyue Tagne tell me to send a kiss to you,
Best,
DGS
[cid:image001.png at 01CD52C2.E1AE1DF0]
David GARCIA-SANCHEZ
greenaffair
Tel. +33 (0)1 46 03 22 66
Mobile +33 (0)6 78 15 08 09
130-136 rue de Silly - CS 90071 – 92773 Boulogne-Billancourt Cedex
www.greenaffair.com<http://www.greenaffair.com/>
De : Julien Marrec [mailto:julien.marrec at gmail.com]
Envoyé : Tuesday, February 24, 2015 11:22 AM
À : David GARCIA SANCHEZ
Objet : Re: [Bldg-sim] LEED v4 ligthing devices
Vu !
C'est bon pour le 9.4.1.2. What it says it that you have at least one control device (not 24 hrs operation...) and that you need one control step between 30% and 70% (Off/mid/on). Also, IF you happen to have manual devices, they need to be readily accessible.
In your case, the primary control is daylight/occupancy dimming, and you do have more than one control step between 30% and 70%, so I think you're good.
As far as the parking garage goes, not sure.
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13
LinkedIn (en) : www.linkedin.com/in/julienmarrec<http://www.linkedin.com/in/julienmarrec>
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr<http://www.linkedin.com/in/julienmarrec/fr>
2015-02-24 10:14 GMT+01:00 David GARCIA SANCHEZ <dgarciasanchez at greenaffair.com<mailto:dgarciasanchez at greenaffair.com>>:
Hi all,
Hope you are doing well,
I have two specific questions concerning the interpretation of ASHRAE standard 90.1-2010 for LEED v4, mandatory provisions for lighting and I hope you can help me. (my project is a classic LEED CS office building in the center of Paris)
The first one is concerning space control. The standard states that each manual devices should have the a) requirement (see below). So my doubt is concerning the “manual” word. It seems that it should be a control step with the “manual interrupters” to three levels (on/middle/off) instead of the classic two levels interruptors? (on/off)? Because, specifically in my project we have natural light dimming/occupant sensor and BMS so I didn’t see the interest of put three levels interrupters if the light will be graded with natural light after the lighting device turn on. I’m obliged then to put three levels interrupters in all my project even that I have dimming/occupancy sensors and BMS?
[cid:image006.png at 01D05026.BE3EA420]
The second question is concerning Parking garage lighting control (point 9.4.1.3.b. of Ashrae standard 90.1-2010)
[cid:image007.png at 01D05026.BE3EA420]
In our project we have 1/3 2/3 rule for parking areas. It means that all time at least 1/3 of total luminaires are always ON (the rest are off) unless an occupant is detected within the area, in that case the rest 2/3 of luminaires turns ON. Which is stated in the point b of previous mandatory provisions is that “each” luminaire power should be reduced. Which is impossible with previous system that is very common in France for security reasons. So I need to change my system conception or I can do something? Or I misunderstood the point?
Thanks in advance for all your answers,
Regards,
[cid:image001.png at 01CD52C2.E1AE1DF0]
David GARCIA-SANCHEZ
greenaffair
Tel. +33 (0)1 46 03 22 66<tel:%2B33%20%280%291%2046%2003%2022%2066>
Mobile +33 (0)6 78 15 08 09<tel:%2B33%20%280%296%2078%2015%2008%2009>
130-136 rue de Silly - CS 90071 – 92773 Boulogne-Billancourt Cedex
www.greenaffair.com<http://www.greenaffair.com/>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150224/f8891aca/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 29423 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150224/f8891aca/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 5833 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150224/f8891aca/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 74811 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150224/f8891aca/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 66733 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150224/f8891aca/attachment-0003.png>
    
    
More information about the Bldg-sim
mailing list