[Bldg-sim] Swimming pool lighting with 90.1
Elizabeth Gillmor
elizabeth at energetics-eng.com
Thu Jun 4 12:47:03 PDT 2015
What I have typically done for outdoor pools under 2007 is classify the
entire pool and deck as "plaza/special feature". That usually seems to be
more than enough, and I can usually claim a bit of savings too. But Nick's
approach also seems very reasonable; you could certainly call it exempt as
an athletic playing field, especially if you have a lap pool. That seems
to be supported by the language in 2010.
*Elizabeth Gillmor PE, LC, LEED AP*
*e n e r g e t i c s **consulting engineers, llc*
energetics-eng.com
c 303.619.0091
On Thu, Jun 4, 2015 at 12:47 PM, Nicholas Caton <ncaton at catonenergy.com>
wrote:
> Cam and Elizabeth are right, I did not pick up with certainty in my first
> reading that both cases were indoor, so I figured it might be appropriate
> to point out pools are more explicitly addressed on the exterior side of
> things.
>
>
>
> With the understanding the pools are definitely located in interior
> spaces, you’re definitely going to be safer sticking to the indoor
> approaches if that produces acceptable results.
>
>
>
> Space-by-space is naturally likely to produce better results if you can
> justify any of the higher Class LPD’s.
>
>
>
> ~Nick
>
>
>
>
>
> *NICK CATON, P.E.*
> *Owner*
>
>
>
> *Caton Energy Consulting*
> 1150 N. 192nd St., #4-202
>
> Shoreline, WA 98133
> office: 785.410.3317
>
> www.catonenergy.com
>
>
>
> *From:* Elizabeth Gillmor [mailto:elizabeth at energetics-eng.com]
> *Sent:* Thursday, June 04, 2015 10:31 AM
> *To:* Cam Fitzgerald
> *Cc:* Julien.Dutel at mern.gouv.qc.ca; ncaton at catonenergy.com;
> bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Swimming pool lighting with 90.1
>
>
>
> Former lighting designer here.
>
>
>
> You should use the "gymnasium" number, and use a space by space calc. If
> you think about it, a natatorium is the same space size/volume and
> occupancy as a gym, with similar footcandle requirements for both
> recreation and competition. I have successfully used this on many LEED
> EAc1 submittals. Electrical engineers for these projects use the gymnasium
> number for COMCheck as well. It's definitely the norm.
>
>
>
> Good luck!
>
> Elizabeth
>
>
> *Elizabeth Gillmor **PE, LC, LEED AP*
>
>
>
> *e n e r g e t i c s **consulting engineers, llc*
>
> energetics-eng.com
>
> c 303.619.0091
>
>
>
> On Thu, Jun 4, 2015 at 10:30 AM, Cam Fitzgerald <fitzgerald at sevengroup.com>
> wrote:
>
> Hello Julien,
>
>
>
> Usually, Nick’s advice is spot on, but I have to disagree that it would be
> appropriate to apply an exception for exterior lighting to an indoor pool.
> I expect the exclusion for outdoor playing fields, etc relates to light
> pollution limitations, allowing player safety to supersede the
> restrictions. This would be akin to using the parking garage and parking
> lot lighting to be sued interchangeably. Keep in mind that exterior
> lighting is a mandatory provision and interior lighting is a prescriptive
> measure – apples and oranges. I think you are on the right track with the
> gymnasium alternatives. Section 3 includes specific definitions for
> interior versus exterior spaces and that should be what determines whether
> you use Table 9.4.5 or 9.5.1/9.6.1.
>
>
>
> Just my 2 cents J
>
>
>
>
>
> Cam Fitzgerald
>
>
>
> Energy Opportunities/a 7group company
>
>
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
> Behalf Of *Julien.Dutel at mern.gouv.qc.ca
> *Sent:* Thursday, June 04, 2015 12:13 PM
> *To:* ncaton at catonenergy.com; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Swimming pool lighting with 90.1
>
>
>
> Hi Nick,
>
>
>
> The question was for a demonstrating prescriptive compliance.
>
> Thanks for your quick and detailed answer (I’m really surprised that we
> could invoke an outdoor lighting exception for an interior lighting!)
>
>
>
> Julien
>
>
>
> *De :* Nicholas Caton [mailto:ncaton at catonenergy.com
> <ncaton at catonenergy.com>]
> *Envoyé :* 4 juin 2015 11:54
> *À :* Dutel, Julien (BEIE); bldg-sim at lists.onebuilding.org
> *Objet :* RE: [Bldg-sim] Swimming pool lighting with 90.1
>
>
>
> Hi Julien,
>
>
>
> For either case, and even if the pools are interior to the building, I
> would consider citing “Lighting for swimming pools and water features” is
> under the exempted list for exterior lighting power calculations under
> 90.1-2010, and more broadly “athletic playing areas” under 90.1-2007.
>
>
>
> Evoking that exception, you could
>
> A) have the baseline match the proposed (for a PRM model),
>
> B) omit that lighting power entirely (for demonstrating prescriptive
> compliance), or else
>
> C) the stage is then set for you to differentiate from the baseline
> by demonstrating how your design saves energy relative to “standard” pool
> lighting by way of separate/exceptional calculations.
>
>
>
> If you want to wrap into your interior LPD regardless,
>
> 1. Gymnasium/Sports Arena/Exercise Center seem to be the likely
> candidates for BAM.
>
> 2. Class I through Class IV comes from IESNA Handbook/RP-6, and is
> used to differentiate illuminance recommendations based upon the degree of
> competition (ranging from professional/national at Class I down to
> amateur/recreational at class IV). I’d suggest having your lighting
> designer determine which set of illumination recommendations best matches
> the photometric calculations for pool surface/deck surface illumination.
>
>
>
> ~Nick
>
>
>
> *NICK CATON, P.E.*
> *Owner*
>
>
>
> *Caton Energy Consulting*
> 1150 N. 192nd St., #4-202
>
> Shoreline, WA 98133
> office: 785.410.3317
>
> www.catonenergy.com
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
> Behalf Of *Julien.Dutel at mern.gouv.qc.ca
> *Sent:* Thursday, June 04, 2015 7:42 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Swimming pool lighting with 90.1
>
>
>
> Hello,
>
>
>
> I have two concrete cases where I’m embarrassed regarding lighting in a
> swimming pool with 90.1.
>
>
>
> *Case 1 : A swimming pool building (the building is a swimming pool)*
>
> In the lighting section of 90.1, the Building Area Method (9.5) has no
> building area type corresponding specifically to a swimming pool. My guess
> would be to choose the “Gymnasium” because as a swimming pool, there is
> high ceiling and locker room.
>
>
>
> Using the Building Area Method, is the “Gymnasium” a correct assumption
> for a swimming pool building ?
>
>
>
> *Case 2 : A swimming pool in a residential building*
>
> Assuming that the “multifamily”’s LPD doesn’t allow me to comply to the
> Building Area Method, and I decide to choose the space by space method. My
> guess would be to choose a building-specific space type in the list “Sport
> Arena”, but I’m block by these unanswered question
> <http://energy-models.com/forum/energy-modeling-software/trace-700/leed-and-ashrae-901/lighting-power-density-space-space-meth>
> : what is the meaning of the class ? :
>
> · Court sport arena – class 4
>
> · Court sport arena – class 2
>
> · Court sport arena – class 1
>
>
>
> Using the Space by Space Method, what would be the best building-specific
> space type for the area dedicated to the pool ?
>
>
>
>
>
> Thanks,
>
>
>
> Julien
>
>
>
> *Julien Dutel,* ing., CEM, CMVP*.*
>
> Direction des secteurs résidentiel, institutionnel et des affaires
>
> Bureau de l'efficacité et de l'innovation énergétiques
>
> Ministère des Ressources naturelles
>
> 5700, 4e Avenue Ouest, B-406
>
> Québec (Québec) G1H 6R1
>
> Téléphone : 418 627-6379, poste 8060
>
> Téléphone sans frais : 1 877 727-6655
>
> Télécopieur : 418 643-5828
>
> http://www.efficaciteenergetique.mrn.gouv.qc.ca
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150604/6e4a51e6/attachment.htm>
More information about the Bldg-sim
mailing list