[Bldg-sim] Baseline case pressure drop credit calculation
Duggin, Cory
Cory.Duggin at tlc-eng.com
Mon Mar 9 14:21:39 PDT 2015
Yes, you only get to take the pressure drop adjustment for baseline systems serving spaces that are served by the MAU in your proposed. I have even been asked to only apply the PD to the amount of airflow the system with the filter supplies, but this was in a situation where the amount of return air very high in comparison.
Cory Duggin, PE, LEED AP BD+C
Associate/Energy Engineer
TLC Engineering for Architecture
direct:
615-346-1939
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Monday, March 09, 2015 4:14 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Baseline case pressure drop credit calculation
A question about pressure drop credit calculation:
Table 6.5.31.1B lists the pressure drop adjustment values. My example is a zonal system (fan coils, heat pumps, etc.). Outdoor air is ducted from an ERV make-up air system to each zonal system. The make-up air system has a heat recovery device and a MERV 13 filter. Does one take credit for the devices on the make-up air system when calculating the baseline fan power for the respective systems?
As only a fraction of the supply flow of the zonal systems comes from the make-up air system, it seems inappropriate to take credit for devices on the make-up air system?
Christopher Jones, P.Eng.
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150309/43e66814/attachment.htm>
More information about the Bldg-sim
mailing list