[Bldg-sim] Use of simulation for ASHRAE 62.1 for compliance.
Wealend, Edwin
e.wealend at cundall.com
Sun Mar 22 18:35:14 PDT 2015
Hi Hema,
For the last natural ventilation design I had reviewed, Nathan’s suggestions are sensible – using an annual simulation and bulk airflow modelling within a software such as IES or TAS. Our reviewer requested a further 3-4 steady state CFD simulations using boundary conditions calculated in the bulk airflow model at typical times (including velocities/temperatures at openings calculated based on the same annual climate data used for the energy modelling). These CFD simulations were taken at typical times of the year to show that both mean age of the air wasn’t too high (i.e. that there were no occupied areas that the fresh air was not reaching), and that the temperatures in the spaces as a result of a natural ventilation strategy were not too cold.
Essentially you need to prove that you will achieve the fresh air rates required, without sacrificing comfort and use the CFD to prove the fresh air distribution is acceptable. I wouldn’t say you need to show significantly higher ventilation rates – in winter this would be a significant energy penalty, and you would expect to meet the minimum standard – however, due to the un-predictable nature of the wind, we took the approach of proving that the minimum ventilation in the occupied period always exceeded the requirements of a DOAS mechanical system. This was acceptable to our reviewer.
Unfortunately, 62.1-2007 is not a good tool for passive design – It’s very much a worst case set of criteria.
Hope that helps,
Ed
Edwin Wealend
Principal Engineer
Cundall Engineering Design Consulting (Shanghai) co., Ltd
宽德工程设计咨询(上海)有限公司
T +86 021 5836 6138
F +86 021 5836 6137
www.cundall.com.cn<http://www.cundall.com.cn/>
[cid:image004.png at 01D051A9.19F16E00]<http://www.linkedin.com/company/cundall> [cid:image007.png at 01D051A9.19F16E00] <http://twitter.com/#!/cundall_global>
Suite 2102, 21/F, Longyu Tower, 1036 South Pudong Road, Pudong, Shanghai, 200120, P.R.China
上海市浦东新区浦东南路1036号隆宇大厦2102室 邮编: 200120
Please consider the environment before printing this e-mail
From: Nathan Miller [mailto:nathanm at rushingco.com]
Sent: 20 March 2015 21:17
To: Hema Sree Rallapalli; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Use of simulation for ASHRAE 62.1 for compliance.
Hema,
It’s been a while since I documented a natural ventilation project for LEED (I’m assuming you are doing this for LEED?), but in the past (LEED-NC v2.2 era), I’ve used annual natural ventilation simulation results (TAS and IES Virtual Environment are a couple of tools that work) to show that both peak and typical natural ventilation air flow rates are SIGNIFICANTLY higher than the requirements if the building used a mechanical ventilation scheme. My impression of CFD is that it is more of a snap-shot in time rather than giving you results across a time-period, so maybe you could demonstrate flow on a peak day and maybe a “stagnant” day to help present your design. Otherwise I’d recommend presenting results from an annual (or natural-ventilation-season) simulation.
Maybe people who have submitted nat vent designs for review in the more recent past can provide more insight.
Sincerely,
Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com<http://www.rushingco.com/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Hema Sree Rallapalli
Sent: Friday, March 20, 2015 2:33 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Use of simulation for ASHRAE 62.1 for compliance.
Dear All,
We are working on a project where we want to make the building naturally ventilated as per ASHRAE 62.1-2007
The prescriptive requirements for natural ventilation are as follows:
* Naturally ventilated spaces must be permanently open to and within 25 ft (8 m) of operable wall or roof openings to the outdoors, the openable area of which is a minimum of 4% of the net occupiable floor area being naturally ventilated. (The net occupiable floor area is measured from the inside surfaces of the walls, excluding permanently enclosed obstructions such as shafts and columns.
* Where interior spaces without direct openings to the outdoors are ventilated through adjoining rooms, the opening between rooms must be permanently unobstructed and have a free area of not less than 8% of the area of the interior room nor less than 25 ft² (2.3 m²).
We have square floor plate of 1000 square meter. As per ASHRAE 62.1 only the perimeter area with a depth of 8 meter can be considered as naturally ventilated space. But we have designed the windows and positioned the windows in order to encourage cross ventilation and we can show sufficient distribution of air by doing CFD simulations. Are the CFD simulations enough to prove that this building is compliant with ASHRAE 62.1 as a naturally ventilated building?
Thanks for your time.
Hema.
For further information about Cundall please visit http://www.cundall.com/Locations/Asia/Asia.aspx
--------------------------------------------------------------------------------
Cundall Engineering Design Consulting (Shanghai) Co Ltd. Registered office: Suite 2102, 21/F, Longyu Tower, 1036 South Pudong Lane, Pudong, Shanghai 200120,
P R China.
All information contained in this email is private and confidential, and may also be privileged.
This email and its attachments are intended solely for the use of the addressee only and if any third party whatsoever
comes into possession of this email,they rely on it at their own risk and Cundall accepts no duty or responsibility
(including in negligence) to any such third party.
If you have received this email in error, please immediately notify the sender and delete all copies from your system.
Privacy Policy: Use of this email and any attachments is subject to the terms on our Website at
http://www.cundall.com/Misc/Privacy-Policy.aspx If you cannot access these terms,
please email terms at cundall.com with SEND TERMS in the subject heading or telephone +44 (0191) 213 1515 and we will send you a copy.
All of our business is conducted in accordance with Cundall’s Ethical Business Policy. http://www.cundall.com/Knowledgehub/Ethical-Business-Policy.aspx
--------------------------------------------------------------------------------
This email message has been scanned for viruses by Mimecast. For more information please visit http://www.mimecast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150323/1d96abbb/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 349 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150323/1d96abbb/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 292 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150323/1d96abbb/attachment-0001.png>
More information about the Bldg-sim
mailing list