Its in Chapter 14 of the 2013 Fundamentals. You can see an example in
Table 1, page 14.2. Third section is Extreme Annual Design Conditions with
min/max extremes for N=5, 10, 20, and 50 years.
For your specific location, you'll have to open up the CD-ROM that comes
with the Handbook. The data in the Appendix (pages 14.19--> ) is a subset
of what can be found for each individual location on the CD-ROM.
On Fri, May 29, 2015 at 10:59 AM, RobertWichert <robert at wichert.org> wrote:
> Good morning to all...
>
> I have gone through what feels like every page of the ASHRAE Handbook of
> Fundamentals in search of "N=20" and N=50" extreme high temperature data.
> I was told it was in the Handbook, but I cannot find it and I have spent
> the better part of two hours looking for it. Numerous web searches have
> not yielded any results either. If anyone is willing to help with this, I
> would very much appreciate it. The job is for a data center, and they need
> the N=20 (described as a twenty year high temperature) and the N=50
> (described as a fifty year high temperature) for design.
>
> Any ideas? Anybody?
>
>
> Thanks!
>
>
> --
> Robert P. Wichert P.Eng. LEED AP
> CEPE CEA HERS I/II BPI BA
> +1 916 966 9060
> FAX +1 916 966 9068
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150529/598a83b7/attachment.htm>
More information about the Bldg-sim
mailing list