Re: [EnergyPlus_Support] People Latent Heat Gain -- slightly more info
At 11:40 AM 8/7/02, Linda Lawrie wrote:
>The short answer (from looking at the code) is that the
>
>TotalPeopleGain = Number of Occupants * Activity Level (activity level is
>input as an hourly schedule value)
>
>Sensible People Gain is then a combination of internal coefficients applied
>to the activity level and the current mean air temperature in the zone
>
>Finally, the Latent is Total - Sensible.
>
>I will have to do a bit more work to get you the source and derivation of
>the internal coefficients.
A little more looking at the code tells me:
! THE FUNCTION IS BASED ON A CURVE FIT TO DATA PRESENTED IN
! TABLE 48 'HEAT GAIN FROM PEOPLE' OF CHAPTER 1 OF THE
'CARRIER
! HANDBOOK OF AIR CONDITIONING SYSTEM DESIGN',
1965. VALUES OF
! SENSIBLE GAIN WERE OBTAINED FROM THE TABLE AT AVERAGE
ADJUSTED
! METABOLIC RATES 350, 400, 450, 500, 750, 850, 1000, AND
! 1450 BTU/HR EACH AT TEMPERATURES 82, 80, 78, 75, AND 70F.
! SENSIBLE GAINS OF 0.0 AT 96F AND EQUAL TO THE METABOLIC RATE
! AT 30F WERE ASSUMED IN ORDER TO GIVE REASONABLE VALUES
BEYOND
! THE REPORTED TEMPERATURE RANGE.
Linda
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Will You Find True Love?
Will You Meet the One?
Free Love Reading by phone!
http://us.click.yahoo.com/it_ffB/R_ZEAA/Ey.GAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/