Re: [EnergyPlus_Support] Total Electric cons.
To report the master meter for the entire building including HVAC
equipment, add the following to your input file:
report meter, electricity:facility, hourly;
(or monthly, or environment)
To see just the electric consumption of the chiller, add this:
report variable, *, Chiller Electric Consumption, hourly;
See the Input Output Reference, pp. 530-537 for more information.
On 17 Sep 2002, at 2:17, atri@xxxxxxxxxxxxxxxxxx wrote:
> If the building electric consumption is only depend on the lighting
> and the electric equipment, then where can i input the chiller and
> chilled water pump electric consumption to effect the building total
> electric consumption? because if i change the nominal capacity in
> CHILLER:ELECTRIC, the result on total building electric consumption
> doesn't change at all!. what is the effect of CHILLER:ELECTRIC in this
> building simulation?
>
> thanks
>
> Atri
>
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Plan to Sell a Home?
> http://us.click.yahoo.com/J2SnNA/y.lEAA/MVfIAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Home Selling? Try Us!
http://us.click.yahoo.com/QrPZMC/iTmEAA/MVfIAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/