Re: [EnergyPlus_Support] Help!
The error message is a little misleading:
** Severe ** Invalid Air Loop Component Type=FAN:SIMPLE:CONSVOLUME
** ~~~ ** Occurs in Component=SUPPLY FAN 1
The error is actually in the BRANCH object which references supply
fan 1:
BRANCH,
Air Loop Main Branch, !- Branch Name
1.3, !- Maximum Branch Flow Rate {m3/s}
FAN:SIMPLE:ConsVolume, !- Comp1 Type
Supply Fan 1 , !- Comp1 Name
The comp1 type is misspelled. It should be FAN:SIMPLE:ConstVolume.
Most error messages of this type can be located by searching your
file for the invalid string.
Mike
On 17 Sep 2002, at 7:49, atri@xxxxxxxxxxxxxxxxxx wrote:
> I Need Help with this building simulation,
> there is error with the "FAN:SIMPLE:ConstVolume" section (as in the
> err message) but i can't figure out what's wrong with this building
> simulation, can't any one help me to find out what wrong with this
> building simulation, i would gratefully with any help.
>
> with this e-mail, i attached the zipped file of my building
> simulation.
>
> Thanks
>
> Atri
> ITB
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Home Selling? Try Us!
> http://us.click.yahoo.com/QrPZMC/iTmEAA/MVfIAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
4 DVDs Free +s&p Join Now
http://us.click.yahoo.com/pt6YBB/NXiEAA/MVfIAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/