No.  "IR Hemispherical Emissivity" is a surface property which 
applies to longwave (infrared, IR) radiant exchange.  If I understand 
your question correctly, you are trying to set absorption of energy 
within the glass thickness to zero.  For longwave infrared, this 
property is controlled by "IR Transmittance at Normal Incidence".

Mike