[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] New file uploaded to EnergyPlus_Support
> Thank you, your answer. I saw the answer for you to send. But your
> answer is not the fact that I want to know. I want to know the
> next fact.
> 1. Although Outdoor DB Temperature is higher than Mean Air
> Temperature, Why is cooling load zero ?
Turn on the surface temperature reporting. At night, the ODB is 26-27C,
but all surfaces will be cooled by night sky radiant transfer. The outside
surface temperature of the roof is approximatley 22C, and the outside
surface of the walls are all slightly below 24C. So there is no cooling
load.
> 2. Although I fix the Mean Air Temperaure by Purchased Air, Why
> does the Mean Air Temperature change ?
Your heating setpoint is 20C, and your cooling setpoint is 24C. When there
is no need for heating of cooling the zone temperature will float in
between.
> 3. If the wall thickness of a material property changed from 0.01m
> to 0.3m, the cooling load is not zero and Mean Air Temperature is
> fixed. Why does the matter occur ?
Thermal mass stores heat from the day so that there is now a cooling load
all night long.
Mike
On 25 Nov 2002, at 1:34, EnergyPlus_Support@xxxxxxxxxxxxxxx wrote:
>
> Hello,
>
> This email message is a notification to let you know that
> a file has been uploaded to the Files area of the EnergyPlus_Support
> group.
>
> File : /Problem_Submittals/question/gagamere
> Uploaded by : gagamere <gagamere@xxxxxxxxxxx>
> Description : question
>
> You can access this file at the URL
>
> http://groups.yahoo.com/group/EnergyPlus_Support/files/Problem_Submitt
> als/question/gagamere
>
> To learn more about file sharing for your group, please visit
>
> http://help.yahoo.com/help/us/groups/files
>
> Regards,
>
> gagamere <gagamere@xxxxxxxxxxx>
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/