Hello,
To answer your question quickly, it is no.  Purchased Air does not have the 
capability to control the humidity ratio at its exit and the exiting 
humidity ratio is specified in the input file.  Purchased Air adjusts the 
capacity of either its heating or cooling at a given leaving humidity 
ratio.  Purchased Air was intended to be a sizing component.

To attain humidity control you would have to specify a system such as the 
"Desiccant Constant Volume Reheat System".  This is DesiccantCVRh.idf in 
our test suite.

Thanks
Dr. Richard Liesen
Associate Director, Building Systems Laboratory
Department of Mechanical and Industrial Engineering
University of Illinois at Urbana-Champaign


At 10:55 AM 1/22/2003, you wrote:
>Hi All;
>
>Can anyone tell me if its possible to specify humidity conditions to be
>attained within a zone, as well as temperature, using the PURCHASED AIR
>ventilation model. So far I've specified a room humidistat but it doesn't
>seem to interact, or is overwritten by the temperature control set point.
>
>Any help would be useful.
>
>Thanks
>
>Dr Umesh Patel
>Consultant
>Buro Happold
>Brodricks Building
>51 Cookridge St
>Leeds, LS2 3AW
>T: 0113 204 2215 (direct line)
>T: 0113 204 2200 (switchboard) ext 6143
>M: 0776 970 1432
>F: 0113 204 2201
>E: umesh.patel@xxxxxxxxxxxxxxx
>
>This transmission is confidential and intended solely for the person or
>organisation to whom it is correctly addressed. If you are not the intended
>recipient of this transmission, you should not take any action in reliance
>on it. Further, this transmission may contain confidential design and other
>information owned by Buro Happold. You should not copy, distribute, use,
>offer for sale or hire such information or in any way infringe the design
>and intellectual property rights of Buro Happold.
>
>It is intended that communication by email from Buro Happold or its
>employees is limited to communications connected to the services provided by
>Buro Happold. Buro Happold accepts no liability for any communications not
>connected to the services it provides.
>
>Computer viruses may be transmitted or downloaded onto your computer system
>via email communication. It is the recipient's responsibility to take any
>action necessary to prevent computer viruses being transmitted in this way.
>Accordingly, Buro Happold disclaims all responsibility which arises directly
>or indirectly from such transmission of computer viruses.
>
>
>
>
>[Non-text portions of this message have been removed]
>
>
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/



To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/