Isidor,
Actually, what I think has happened is that there are too many references
in the IDD. I just looked under those coils and for the Part Load we have:
A9 , \field Part Load Fraction Correlation (function of part load ratio)
\required-field
\type object-list
\object-list QuadraticCurves
\object-list CubicCurves
\note quadratic curve = a + b*PLR + c*PLR**2
\note cubic curve = a + b*PLR + c*PLR**2 + d*PLR**3
\note PLR = part load ratio (cooling load/steady-state capacity)
If you want to just delete the line:
\object-list CubicCurves
under the two coils, you will be okay. And we will try to fix it
appropriately for the next release. I think (Mike and/or Jason probably
aren't on line yet) that you can't reference two object lists here. You
can make a name go to two different lists (our \reference field) but can't
do this.
Thanks for catching it -- sorry for the inconvenience. (I can also upload
a new "V1-0-3" Energy+.idd, if you would prefer.)
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/