Dear all, 

I had a look at Franzs model and turned off the heating, so that there was just the cooling option on. So I got the failure

** Warning ** COIL:DX:CoolingBypassFactorEmpirical "MAIN COOLING COIL ZONE001" - Air volume flow rate per watt of rated total cooling capacity is out of range 

too. Looking at all his nodes, I couldn't find anything which could be wrong as Mike mentioned in the mornig. In former days there was a mismatch but we had corrected this for him - you remember. Also changing the rate of cooling capacity didn't make a real difference. Sometimes you get more or less warnings, depending on the rate. 

For me it seems that the error occours the first time when the cooling starts operating. I run different clima files with the same idf-file from Franz and got only the mentioned error message when cooling was needed.

Does anybody know if AUTOSIZING could help in Franzs case to solve his problem?

So have a nice weekend

Isidor

>>> eglyon@xxxxxxx 02/14 3:03  >>>
I have had some problems with this warning if the inlet conditions are too warm.  The EnergyPlus loops are mass flow calculated on initial standard air conditions.  If you have a very hot zone and turn on a dx cooling that normally works fine, the volume flow for mass flow at high temp can exceed the unit design rate.

Is there a time table for integrating real fans with constant volume to replace simple fans with constant mass flow? 

Ned Lyon

Senior Staff Engineer
Simpson Gumpertz & Heger Inc.

41 Seyon Street
Building #1, Suite 500
Waltham, MA  02453

Phone:  781-907-9000
Fax:  781-907-9009


>>> mjwitte@xxxxxxxx 02/13/03 05:58PM >>>




To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov 

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/ 

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/ 




------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/FpY02D/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/