Re: [EnergyPlus_Support] Zone Separation



Alexander:

There is no requirement that two corresponding interzone surfaces be 
adjacent to each other.  For interzone surfaces, the heat balance 
merely assigns the inside face temperature as the outside face 
temperature of the corresponding surface.  So the area of the 
surfaces should match in order to conserve energy.  And warnings will 
be issued if the tilt and azimuth of the two surfaces do not mirror 
each other.

Mike


On 14 Feb 2003, at 11:42, alexander.beisteiner@xxxxxxxxxxxxxxxxxx wrote:

> Dear E+ User
> Simulating a multiple zone building, is it necessary that zones or
> walls have to touch each other geometrically in order to simulate heat
> transfer? Or, is it possible to place zones anywhere in the building
> and reference heat transfer walls of adjacent zones, although zones
> geometrically do not touch each other.
> 
> I am looking forward to your reply.
> 
> Alexander
> 
> 
> ----------------------------------------------
> DI (FH) Alexander Beisteiner
> Forschungs- und Technologietransfer
> Pinkafeld GmbH
> Steinamangerstrasse 21
> 7423 Pinkafeld
> 
> Tel.: 0043/3357/45370-1324
> alexander.beisteiner@xxxxxxxxxxxxxxxxxx
> http://www.fh-pinkafeld.ac.at
> 
> 


========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/FpY02D/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/