[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] inside surfaces
See answers below.
On 28 Feb 2003, at 16:45, santuta santuta@xxxxxxxxx wrote:
>
> Hello again,
>
> I am trying to simulate a generic office in the middle of a building.
> For this I used "OtherZoneSurface" for all the interior surfaces
> (including roof and floor) and used each interior surface as exterior
> environment for itself, since all the building would be conditioned at
> approximately the same temperature. Doing this I got very close inside
> and outside temperatures for these surfaces. However I have problems
> understanding a couple of results:
>
> 1-Although the I-O temperatures are quite close, they`re not equal as
> I would expect. Is this normal?
A slight difference is normal, because the outside surface heat
balance is done once at the beginning of the time step and then the
inside heat balance iterates.
>
> 2-The conduction through these surfaces (which I would like to be
> zero) is quite high compared to exterior surfaces. I am using "Opaque
> Surface Inside Face Conduction", and the relation between deltaT, U-
> value and conduction seems inconsistent. For instance, a typical
> temperature difference for interior surface is between .3C and 1.3C,
> for exterior surfaces is up to 12C. However, the conduction remains in
> the same order of magnitude, even if I choose a higher U-value for the
> exterior wall. How can this be possible?
"Opaque Surface Inside Face Conduction" is the heat flow into/out of
the interior (thermal mass) of the surface. It does not represent
conduction across the surface.
I think we need to rename this output variable, because it causes
much confusion. Suggestions anyone?
>
> 3-I am aware that a solution would be to define these surfaces as
> internal mass, and not as heat transfer, but I am concerned with the
> effects on radiation and daylighting results, that if I omit floor and
> roof might change. Is this correct?
Yes, if you are doing detailed daylighting or full interior solar
distribution.
Mike
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/FpY02D/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/