Ming:
No, it would not be the same. Run Period data is taken from a
weather data file and will almost always not be the same as the
design day data. The design days in the datasets are single days
statistically determined from 30-yr weather data to be used for
equipment sizing. The weather files are a collection of actual
months from a similar (often the same) 30-yr data set. Also, for
autosizing equipment, design days are required. You cannot autosize
based on data from a weather file.
Mike
On 13 Mar 2003, at 22:06, waspoorboy wrote:
> Hi,
>
> RunPeriod defines a period of time for simulation.
> (ex.3/13/2003-4/13/2003)
> DesignDay is an "user created" day (weather) data for simulation.
> ------------ I guess there're different aspects for using these two.
> But I don't quite get it. (To me, in some sense DesignDay is just one
> or more selected day(s) from RunPeriod) ------------ In
> 1zoneuncontrolled.idf, two DesignDay are used. 1/21 and 7/21. Is it
> equivalent to use the following instead ? RunPeriod 1/21-1/21 and
> RunPeriod 7/21-7/21
>
> Thanks,
> Ming
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/