Re: [EnergyPlus_Support] Warning Calculated Humidity Ratio



The message shows that the Dry-Bulb temperature is
below the Wet-Bulb temperature, an impossible
condition. The weather routine should check for this
condition and set the wet-bulb temperature equal to
the dry-bulb temperature whenever wet-bulb temperature
is calculated to be above the dry-bulb temperature.

--- "Richard J. Liesen" <rliesen@xxxxxxxx> wrote:
> Hello Alex,
> 
> What this message is telling you is that the
> calculated humidity ratio is 
> below the physical realm of possibility, a very
> small negative value,  and 
> it is setting it to a very small physical value. 
> Either the dry and wet 
> bulb, or the numerical procedures are slightly off
> at this physical 
> boundary, but either way the warning generated is
> within numerical 
> precision and I doubt that this will cause any
> distortion of results.  The 
> reason that it should not cause any distortion is
> that you are probably in 
> heating scenarios and this is normally all sensible
> heat transfer.
> 
> 
> Thanks Richard Liesen
> 
> 
> At 05:14 PM 4/10/2003, Alexander Beisteiner wrote:
> >Dear E+ User,
> >
> >A weather file simulation of a purchased air system
> produces the
> >following warning message:
> >
> >Program Version,EnergyPlus 1.0.3.019, 10.04.2003
> 15:52
> >    ************* Testing Individual Branch
> Integrity
> >    ************* All Branches passed integrity
> testing
> >    ************* No node connection errors were
> found.
> >    ** Warning ** Calculated Humidity Ratio Invalid
> (PSYWTP)
> >    **   ~~~   ** (mm/dd/hh)=  1/05/01 Dry-Bulb=
> -24.40 Wet-Bulb= -25.40
> >Pressure= 97500.00
> >    **   ~~~   ** Calculated Humidity Ratio=
> -2.3594E-006 ... Humidity
> >Ratio set for a relative humidity ratio of .01
> >    ** Warning ** Calculated Humidity Ratio Invalid
> (PSYWTP)
> >    **   ~~~   ** (mm/dd/hh)=  1/05/01 Dry-Bulb=
> -25.30 Wet-Bulb= -26.30
> >Pressure= 97700.00
> >    **   ~~~   ** Calculated Humidity Ratio=
> -3.6357E-005 ... Humidity
> >Ratio set for a relative humidity ratio of .01
> >    ** Warning ** Calculated Humidity Ratio Invalid
> (PSYWTP)
> >    **   ~~~   ** (mm/dd/hh)=  1/05/01 Dry-Bulb=
> -26.10 Wet-Bulb= -27.10
> >Pressure= 97800.00
> >    **   ~~~   ** Calculated Humidity Ratio=
> -6.3930E-005 ... Humidity
> >Ratio set for a relative humidity ratio of .01
> >    ** Warning ** Calculated Humidity Ratio Invalid
> (PSYWTP)
> >    **   ~~~   ** (mm/dd/hh)=  1/05/01 Dry-Bulb=
> -27.00 Wet-Bulb= -28.00
> >Pressure= 97900.00
> >    **   ~~~   ** Calculated Humidity Ratio=
> -9.2471E-005 ... Humidity
> >Ratio set for a relative humidity ratio of .01
> >    ** Warning ** Calculated Humidity Ratio Invalid
> (PSYWTP)
> >    **   ~~~   ** (mm/dd/hh)=  1/05/01 Dry-Bulb=
> -27.30 Wet-Bulb= -28.30
> >Pressure= 98000.00
> >    **   ~~~   ** Calculated Humidity Ratio=
> -1.0164E-004 ... Humidity
> >Ratio set for a relative humidity ratio of .01
> >    ** Warning ** Calculated Humidity Ratio Invalid
> (PSYWTP)
> >    **   ~~~   ** (mm/dd/hh)=  1/05/01 Dry-Bulb=
> -27.60 Wet-Bulb= -28.60
> >Pressure= 98100.00
> >    **   ~~~   ** Calculated Humidity Ratio=
> -1.1054E-004 ... Humidity
> >Ratio set for a relative humidity ratio of .01
> >    ************* Psychrometric Error Summary
> >    *************  Routine - Number of errors
> >    *************    PSYDPT-0
> >    *************    PSYRHT-0
> >    *************    PSYTWD-0
> >    *************    PSYVTW-0
> >    *************    PSYWDP-0
> >    *************    PSYWTH-0
> >    *************    PSYWTP-363
> >    *************    PSYWTR-0
> >    *************    SATUPT-0
> >    *************    SATUTH-0
> >    *************    SATUTP-0
> >    *************    tp12c0-0
> >    *************    tp12c1-0
> >    *************    tp12h0-0
> >    *************    tp12h1-0
> >    *************    freeze-0
> >    ************* EnergyPlus Completed
> Successfully-- 6 Warning; 0 Severe
> >Errors; Elapsed Time=00hr 00min 13sec
> >
> >Looking at the weather file (of Irkutsk), I could
> not find temperature
> >and pressure values for the time stated: 1/05/01.
> What does the warning
> >tell? Does it distort results? Can the message be
> neglected?
> >
> >I am looking forward to your help.
> >
> >Alexander
> >
> >_______________________________________
> >DI (FH) Alexander Beisteiner
> >Wissenschaftlicher Mitarbeiter
> >
> >Forschungs- und Technologietransfer Pinkafeld GmbH
> >Steinamangerstraße 21
> >A - 7423 Pinkafeld
> >Tel.: +43-3357-45370 DW 1324
> >Fax.: +433357-45370 DW 1010
> >
> >
> >
> >
> >
> >[Non-text portions of this message have been
> removed]
> >
> >
> >
> >To unsubscribe from this group, send an email to:
> >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any
> files to the appropriate 
> >folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> >Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
> 
> 
> 


__________________________________________________
Do you Yahoo!?
Yahoo! Tax Center - File online, calculators, forms, and more
http://tax.yahoo.com

------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/VygGAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/