Re: [EnergyPlus_Support] heating/cooling at same time
At 04:11 PM 5/30/2003, idoebber wrote:
>Thank you for those that replied to my email. Unfortunately, my reporting
>frequency of my data is every time step (10 minutes since I am modeling an
>HVAC system).
The comments are still applicable. You are reporting at the "zone time
step". The HVAC may have several time steps beneath that time step. To
see each and every time step, you need to report at the "detailed" level.
Detailed is the each and every calculation time step. Remember that the
HVAC time step is/can be variable and go down to a minute until things are
resolved. I will add a "memo" or "note" to the report variable command so
that this is more clear.
Report Variable,
\memo each Report Variable command picks variables to be put onto
the standard output file (.eso)
\memo some variables may not be reported for every simulation
A1 , \field Key_Value
\default *
\note use '*' (without quotes) to apply this variable to all keys
A2 , \field Variable_Name
\required-field
A3 , \field Reporting_Frequency
\type choice
\key detailed
\key timestep
\key hourly
\key daily
\key monthly
\key runperiod
A4 ; \field Schedule_Name
\type object-list
\object-list ScheduleNames
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get A Free Psychic Reading! Your Online Answer To Life's Important Questions.
http://us.click.yahoo.com/Lj3uPC/Me7FAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/