Re: [EnergyPlus_Support] strange simulation results



I see several things which may be contributing to this result:

1.  The floor plan is not rectangular, so all zones have some walls 
facing in each direction.  Because of the triangular sections, the 
northern zones may actually have more southerly exposure than the 
southern zones.

2.  The shading from neighboring buildings is not symmetrical.  There 
is much more shading on the west side of the building.

3.  The weather data indicates that solar intensities are often 
higher in the morning than in the afternoon.  If you run a design 
day, you'll see higher loads in the west zones than in the east.  Is 
it common for afternoons to be more cloudy than mornings in 
Singapore?  This may be the primary driver.

Mike


On 8 Jul 2003, at 9:58, sdep1017 wrote:

> Hi,
> 
> I'm running a simplifed case of energy performance in Singapore 
> public housing. The results over a one year run seem to show that east
> facing units are warmer than west facing units, and north warmer than
> south.
> 
> This seems to contradict conventional wisdom that west facing units
> are warmer. Has anyone encountered such results before?
> 
> My idf and weather files have been uploaded in the problem submittal
> section, under the folder named "yijun huang". thanks.
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Inkjet cartridges up to 80% off. HP, Epson,
> Lexmark--we have your brand. Free shipping on every order to the U.S.
> and Canada! Excellent service.
> http://www.c1tracking.com/l.asp?cid=5510
> http://us.click.yahoo.com/QWB0QC/.eUGAA/ySSFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Inkjet cartridges up to 80% off. HP, Epson, Lexmark--we have your brand.
Free shipping on every order to the U.S. and Canada! Excellent service.
http://www.c1tracking.com/l.asp?cid=5510
http://us.click.yahoo.com/QWB0QC/.eUGAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/