[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Return Fan
Problem solved, thank you.
Sam Roose
-----Original Message-----
From: Michael J. Witte [mailto:mjwitte@xxxxxxxx]
Sent: Fri 29/08/2003 6:55 a.m.
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc:
Subject: Re: [EnergyPlus_Support] Return Fan
The return fan is placed as the first component on the main branch of
the air loop, right before the outside air system. I will upload an
example with return fan shortly into the Examples folder in the yahoo
files area.
Mike
On 28 Aug 2003, at 21:00, Samuel Roose wrote:
> I am puzzled about how to specify return air fans as part of an air
> loop. The attached file is an attempt at this based on Figure 43 of
> the Input - Output reference. The intention is to flow through the
> outside air system to supply fans, cooling coil, humidifier, zone and
> then return the air back to the outside air system somehow. The file
> runs fine without the return fans. Has anyone had any success with
> return air fans? If so, please peruse the file (particularly the main
> air loop branch and fans input). I would appreciate any feedback.
> Thanks, Sam Roose Victoria University of Wellington
>
>
> [Non-text portions of this message have been removed]
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
> HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
Yahoo! Groups Sponsor
ADVERTISEMENT
Click Here! <http://rd.yahoo.com/M=244522.3707890.4968055.1261774/D=egroupweb/S=1705007389:HM/A=1595055/R=0/SIG=124j83ehr/*http://ashnin.com/clk/muryutaitakenattogyo?YH=3707890&yhad=1595055>
<http://us.adserver.yahoo.com/l?M=244522.3707890.4968055.1261774/D=egroupmail/S=:HM/A=1595055/rand=821659031>
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> .
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/