[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] using economizer



I am trying to set the CONTROLLER:OUTSIDE AIR, but I found a very strange thing: when I set the EconomizerChoice on NO ECONOMISER the gas facility consumption become the half with respect to the simulation using ECONOMIZER. I can't understand how with the economizer "on" the gas consumption is two time the case without it. Could anyone please help me to understand this behaviour?
Here attached the relative part of my input file.

Thank you very much,
Roberto
!- =========== ALL OBJECTS IN CLASS: CONTROLLER:OUTSIDE AIR ===========

CONTROLLER:OUTSIDE AIR,

outside air controller, !- Name

ECONOMIZER, !- EconomizerChoice

RETURN AIR TEMP LIMIT, !- ReturnAirTempLimit

RETURN AIR ENTHALPY LIMIT, !- ReturnAirEnthalpyLimit

NO LOCKOUT, !- Lockout

FIXED MINIMUM, !- MinimumLimit

oa mixer vendita outlet node, !- Control_Node

oa vendita mixer inlet node, !- Actuated_Node

0.0065, !- minimum outside air flow rate {m3/s}

autosize, !- maximum outside air flow rate {m3/s}

24, !- temperature limit {C}

10, !- temperature lower limit {C}

0, !- enthalpy limit {J/kg}

vendita reliefair mixer outlet node, !- Relief_Air_Outlet_Node

primary air loop vendita inlet node, !- Return_Air_Node

min oa vendita sched; !- Minimum Outside Air Schedule Name



CONTROLLER:OUTSIDE AIR,

outside air controller galleria, !- Name

ECONOMIZER, !- EconomizerChoice

RETURN AIR TEMP LIMIT, !- ReturnAirTempLimit

RETURN AIR ENTHALPY LIMIT, !- ReturnAirEnthalpyLimit

NO LOCKOUT, !- Lockout

FIXED MINIMUM, !- MinimumLimit

oa mixer galleria outlet node, !- Control_Node

oa galleria mixer inlet node, !- Actuated_Node

0.0115, !- minimum outside air flow rate {m3/s}

autosize, !- maximum outside air flow rate {m3/s}

24, !- temperature limit {C}

10, !- temperature lower limit {C}

0, !- enthalpy limit {J/kg}

galleria reliefair mixer outlet node, !- Relief_Air_Outlet_Node

primary air loop galleria inlet node, !- Return_Air_Node

min oa galleria sched; !- Minimum Outside Air Schedule Name



CONTROLLER:OUTSIDE AIR,

outside air controller uffici, !- Name

ECONOMIZER, !- EconomizerChoice

RETURN AIR TEMP LIMIT, !- ReturnAirTempLimit

RETURN AIR ENTHALPY LIMIT, !- ReturnAirEnthalpyLimit

NO LOCKOUT, !- Lockout

FIXED MINIMUM, !- MinimumLimit

oa mixer uffici outlet node, !- Control_Node

oa uffici mixer inlet node, !- Actuated_Node

0.011, !- minimum outside air flow rate {m3/s}

autosize, !- maximum outside air flow rate {m3/s}

24, !- temperature limit {C}

10, !- temperature lower limit {C}

0, !- enthalpy limit {J/kg}

uffici reliefair mixer outlet node, !- Relief_Air_Outlet_Node

primary air loop uffici inlet node, !- Return_Air_Node

min oa uffici sched; !- Minimum Outside Air Schedule Name


[Non-text portions of this message have been removed]


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/