Re: [EnergyPlus_Support] vents



Mohit,

If the self-regulation of the inlet vents is due totally to natural forces I
would model them as COMIS Openings.  There is a problem that at present all
COMIS Surfaces must be associated with a Heat Transfer Surface or
Subsurface, so you would have to define a fictitious window of the
appropriate dimensions and set its heat transfer and solar properties to 0.
Also, make sure its location, especially its height (Z) relative to the zone
that it serves, are input correctly.

Joe

----- Original Message -----
From: "Mohit Mehta" <mohitmehta1@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Tuesday, November 25, 2003 10:42 PM
Subject: [EnergyPlus_Support] vents


> hi:
> i am attempting to model "self regulating inlet vents" as part of the
natural ventilation strategy in a 5 story office building. even though these
inlet vents will be on different floors, they are designed to provide a
relatively constant flow rate over a range of air pressure differences due
to stack effect and external wind conditions.
> does anyone have any suggestions as to how i could go about this in
energyplus?
> is there a specific air-flow component that i could use? or will i have to
trick an opening/crack to achieve this?
> thanks.
> ~mohit
>
>
>
>
> ---------------------------------
> Do you Yahoo!?
> Free Pop-Up Blocker - Get it now
>
> [Non-text portions of this message have been removed]
>
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
>
>
>


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/