Markus:

The typical winter design day assumption is that there is no solar 
radiation present.  This is typically done for sizing purposes since a 
heating system would need to account for days when little or no solar 
radiation was present.  This assumption is not built into EnergyPlus 
though--it is a function of the design day definition.  You can add solar 
radiation to your winter design day by modifying the sky clearness of your 
design day definition.  A sky clearness of 0 means no solar radiation while 
a value of 1 means clear sky (full solar) conditions.  Naturally, you will 
want to run your file with a weather file at some point to see how things 
respond to changing weather/seasons.

Rick Strand

At 05:49 AM 3/15/2004, you wrote:
>Hi, I run a simulation with purchased air to receive the heating and
>cooling rates. My model is a conservatory (large glass surfaces). I
>get cooling rates for the summer but non cooling rates for the
>winter. But the sun radiation into the ZONE produces temperatures of
>40°C in the ZONE and in the winter (I did measurements).
>I need a cooling rate in the winter to calculate the mass of
>required phase change materials to store/release the heat.
>Is the EnergyPlus calculation for the WinterDesignDay without sun
>radiation?
>Thanks Markus
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files are of the Support Web Site.
>
>
>
>
>  -- please post any files to the appropriate folder in the Files are of 
> the Support Web Site.
>
>
>
>
>
>Yahoo! Groups Links
>
>
>
>



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-bit SSL Security!
http://us.click.yahoo.com/LPJzrA/yjVHAA/TtwFAA/dkFolB/TM
---------------------------------------------------------------------~->

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/