Re: [EnergyPlus_Support] Re: radiation data in the epw weather format
In an epw file, hour 12 represents 11:00 am to 12:00 noon. The solar radiation
values for a given hour are the integrated total radiation over the hour in
Wh/m2. For hour 12, the value in the epw file should be the total from 11:00
am to 12:00 noon.
For hourly weather files, EnergyPlus uses this value as the average radiation
rate for the hour in W/m2. The average rate is assumed to occur on the half-
hour, at 11:30 am in this example. Rates for the other time steps in the hour
are determined by interpolation between the half-hour values of the previous or
next time step.
Mike
On 22 Mar 2004, at 15:23, Pc Thomas wrote:
> Hi,
>
> We'd like to find out how the radiation data is handled on an hourly basis for
> the epw format weather file, ie.;
>
> - does the data for hour 11:00 to 12:00noon get integrated from 11:00 to noon;
> or from 11:30am to 12:00pm and then gets assigned to 12:00noon.
>
> Best regards,
> PC
>
> PC Thomas
> Senior Specialist, Arup
> Lvl 10, 201 Kent St.
> Sydney 2000
> t 02 9320 9441 f 02 9320 9321
> m 0417 405 478
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
>
>
>
>
> -- please post any files to the appropriate folder in the Files are of the
> Support Web Site.
>
>
>
>
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/