EnergyPlus controls rely on the load determined by the thermostat. If the
thermostat calls for cooling, the VAV/reheat unit will try to provide that
load. If that means adding reheat to match the requested cooling load, then it
will do so. The terminal unit at that point is not aware of what the zone
thermostat setpoints are, it just knows there is a call for cooling. So, I do
not think you have an error. You can minimize this by resetting the cold deck
temperature.
Mike
On 29 Mar 2004, at 22:00, mikemccarty79 wrote:
> Hi, I am working on a simulation with VAV boxes with electric reheat
> coils and have a controller with a dual setpoint. My setpoints are
> 22.2 and 22.8°C for heating and cooling respectively. I have
> noticed that the reheat coil will turn on but the room temperature
> will still be maintained at the cooling setpoint of 22.8°C. It
> seems that since heat is being added that this should automatically
> go to the lower heating setpoint temperature even if the zone still
> requires some cooling. Since the damper position is already in its
> minimum position, I don't really need all the cooling available by
> my supply air temperature of 15°C. What appears to be happening is
> that the switch to the lower heating setpoint occurs when the
> discharge temperature from the VAV box is above the room temperature
> or at least the cooling setpoint temperature. Is there some error
> in the control scheme for this or is it possible something is set up
> wrong in my simulation. Thanks.
>
> Mike McCarty
> Iowa State University
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
>
>
>
>
> -- please post any files to the appropriate folder in the Files are of the
> Support Web Site.
>
>
>
>
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/