Re: [EnergyPlus_Support] EnergyPlus Holidays



You have "Apply Weekend Holiday Rule" set to Yes.  When this is "yes" and a 
single day holiday falls on the weekend, the "holiday" occurs on the following 
Monday.  My guess is that December 25 is falling on a Sunday and is being 
pushed to Monday the 26th.  Either set the weekend holiday rule to "no", or 
specify a different day of the week for the start day.

Mike
 

On 25 May 2004, at 18:40, Andy Tindale wrote:

> Can anyone explain why the data :
> 
> RunPeriod,
>    12,20,
>    12,30,
>    UseWeatherFile,
>    No,                  ! Use weather file holidays/special day periods
>    Yes,
>    Yes,
>    Yes,
>    Yes,
>    1;
> 
> SpecialDayPeriod, Christmas, December 25, 1, Holiday;
> 
> ...seems to result in December 26 instead of December 25 being simulated as a
> holiday.
> 
> The simulation period is from December 20 2003 to December 30 2003 when December
> 25 is a Thursday.
> 
> The other strange behaviour I am getting is when defining two consecutive single
> day holidays:
> 
> SpecialDayPeriod, Christmas, December 25, 1, Holiday;
> SpecialDayPeriod, Boxing day, December 26, 1, Holiday;
> 
> I get a warning:
> 
> ** Warning ** Special Day definition (BOXING DAY) is overwriting previously
> entered special day period
> 
> Thanks
> Andy Tindale
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/