Re: [EnergyPlus_Support] enthalpy of vaporization of water
In case you're interested in more detail, the EnergyPlus value for heat of
vaporization [J/kg H20] used to convert a latent equipment load into kg of
moisture is computed with the following equation:
2500940.0 + 1858.95*T
Where:
T = Zone dry bulb temperature [C]
Mike
On 8 Jun 2004, at 17:59, Rahul Chillar wrote:
> 2500.94KJ/kg would be most sutiable
> Since this value varies slightly with temperature you might want to look up
> ASHRAE handbook or steam tables to see the required value at the required
> temperature. Energy Plus used values compatible with ASHRAE Handbook of
> fundamentals.
>
> hjunmoon <gt6102a@xxxxxxxxxxxxxxxx> wrote:
> I am converting from latent heat of equipment (W) to rate of water
> vaporized to a zone(kg/s).
> Does anyone know the value of enthalpy of vaporization of water used
> in EnergyPlus?
> Thanks in advance,
>
> Hyeun Jun Moon
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups SponsorADVERTISEMENT
>
>
> ---------------------------------
> Yahoo! Groups Links
>
> To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
>
>
>
>
> Thanks
> Rahul Chillar
> Grad Student
> Building Systems lab
> Univ Of Illinois Urbana Champaign
>
>
> ---------------------------------
> Do you Yahoo!?
> Friends. Fun. Try the all-new Yahoo! Messenger
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/