[EnergyPlus_Support] questions about VAV
I simulate a very small office room (5.1mX2.6mX3.6m) based on HongKong weather data. The mixed air(return air and fresh air) flow through cooling coil and then supply into the room directly. The vav scheme is emplored.
I want to simulate the whole energy consumption in E+. However, some problems puzzle me.
First, I use SINGLE DUCT:VAV:NOREHEAT object and variable speed fan. From the simulation results, flow rate is constant. Of course it is wrong. Then I wonder if variable speed fan can be used to control air flowrate and no VAV duct is used? At this stage, if it can be said that only primary air loop exists and no zone equpiment? I try it, but error message occurs:
** Severe ** Zone Equipment Return Node (Return Air Path or Controlled Zone Equip Configuration) not valid=ZONE OUTLET NODE
** ~~~ ** Occurs in Primary Air Loop=VAV SYS
** Fatal ** Errors found getting Air Primary Loop
Any guy can give me some instructions? Thanks
Xu
----- Original Message -----
From: Xu H.T
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Monday, July 26, 2004 10:00 AM
Subject: [EnergyPlus_Support] about air loop
Dear,
I wonder, in E+, if the air loop and zone equpiment loop are both absolutely necessarily? How about only air loop without zone equpiment loop?
Xu
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Sponsor
ADVERTISEMENT
----------------------------------------------------------------------------
Yahoo! Groups Links
a.. To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
b.. To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
c.. Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/