Re: [EnergyPlus_Support] purchased hot water energy for two systems
The 2 heating components are controlled differently. Right now the
reheat coil operates
during cooling to prevent overcooling. This is a subject of debate as to
whether this is what
we want to be doing.. The baseboard only meets the heating load - so it
is a truer reflection
of the zone heating requirements.
Fred Buhl
pizzaalan wrote:
>Dear all,
>
>I simulated a building equipped with VAV system and reheat coil.
>Then I tried to use baseboard heater instead of reheat coil in all
>the perimeter zones. The purchased hot water energy results for
>these two systems are different. The purchased hot water is the
>only heating source for these two systems, and all the set points,
>schedules, location and constructions are same. The purchased how
>water energy is supposed to represent heating load, right? Why are
>they different for these two systems? Does baseboard heater have
>different heat transfer algorithm with reheat coil?
>
>Thanks.
>
>Alan
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
>Yahoo! Groups Links
>
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/