Re: [EnergyPlus_Support] Daylight
At 01:19 PM 8/3/2004, Fábyo Luiz Pereira wrote:
> I´m trying to simulate a daylight example and have some doubts:
>- "Minimum input power fraction for continuous dimming control"
>(Daylighting:Detailed): This fraction is relative to the "Design Level"
>(Lights)?
Yes -- but you also need to consider the "Lighting Control Type" field.
>- "Total daylighting reference points" (Daylighting:Detailed): I´m afraid that
>can't use 2 reference points, cause the "Daylight Illum at Ref Point"
>Report is
>giving, for some hours, nonsense values like 29000 lux. When I simulate the
>same building with only 1 reference point the results for this report seems to
>be acceptable (maximum value about 2500 lux).
We need to see this input file to see if this is an error in the
code. Please send it to energyplus-support@xxxxxxxx or to me linda@xxxxxxxxxx
>- In my case, I´m using 3025 W of light design level per zone (each one have
>about 150 m2 of floor area), with visible fraction equal to 0.35. This
>way, can
>I estimate a value for my "Illuminance setpoint at first reference point"
>(Daylighting:Detailed)? I´m using the default value for this variable (500
>lux), and I know that usually we choose that based on a table, but I´m not
>sure
>that my power design level can be able to give this illuminance. For my
>viewpoint, knowing the light's visible fraction and the floor area I can
>find a
>illuminance level. Is that right?
You can also produce the "illuminance map" report for your
simulation. Maybe this would help you?
>=====
>________________________________________________________
> Engº Fábyo Luiz Pereira
> UFRGS - Laboratório de Vapor e Refrigeração
> Rua Sarmento Leite, 425 - Sala 203 - Centro - 90050-170
> Fone / Fax: +55 51 3316-3167 / 3316-3355
> www.mecanica.ufrgs.br/lafrig
> Porto Alegre - RS - BRASIL
>
>
>
>
>
>_______________________________________________________
>Yahoo! Acesso Grátis - navegue de graça com conexão de qualidade! Acesse:
>http://br.acesso.yahoo.com/
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files area of the Support Web Site.
>
>Yahoo! Groups Links
>
>
>
>
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/