Re: [EnergyPlus_Support] problems about vav simulation



My apologies for the slow response.  I do not think you will be able to model 
this as described.  EnergyPlus does not have a component to control cooling 
coil bypass.

Mike


On 2 Aug 2004, at 22:50, Xu H.T wrote:

>   Dear
> 
>   I simulate a very simple case: the return air is mixed with the fresh air (the
>   left part of return air is discharged into ourdoor) and then pass through the
>   cooling coil and supply into the room. Using Hong Kong weather data,  I find
>   the humidity in the room is very high.
> 
>   So I change the supply strategy to the following one:
>   The return air is divided into three parts. One is discharged into ourdoor
>   environment like above description. The second part is mixed with the fresh
>   air and then pass through the cooling coil in order to decrease temperature to
>   13â??. The third part of return air is directly mixed with the supply air 
>   from cooling coil (at 13â??)to get the temperature at 19â?? and then supply
>   into the room. For this case, I am puzzled about how to set the primary air
>   loop. Two branches are available? (the third part of return air is bypassed to
>   mix with the lower temperature air from cooling coil). Also, two temperature
>   are set to constant. One is 13â??  from the outlet of cooling coil. The other
>   one is 19â?? for the supply temperature. The SINGLE DUCT:VAV:NOREHEAT is used.
>   How to arrange the control stragegy? 
> 
>   Thanks very much.
> 
>     ----- Original Message ----- 
>     From: Michael J. Witte 
>     To: EnergyPlus_Support@xxxxxxxxxxxxxxx 
>     Sent: Friday, July 30, 2004 2:48 AM
>     Subject: Re: [EnergyPlus_Support] problems about vav simulation
> 
> 
>     My apologies for the delay in diagnosing the problem with this simulation. 
>     The short answer is that the system is undersized, this causes the supply
>     air temperature to be above setpoint and the airflow to the zone increases
>     to the maximum in a failed attempt to meet the zone load.  
> 
>     Why is the system undersized?  
> 
>     1) The system airflow has been sized to exactly meet the design day load
>     (sizing factor = 1.0), but some of the days in the weather file are more
>     extreme than the design day.  
> 
>     2) There is a bug in the chilled water coil sizing in version 1.2.0 which is
>     causing the coil water flow rate to be undersized by approximately 20%.  The
>     easiest solution is to raise the zone sizing factor to approximately 1.2. 
>     The system should then operate as expected.  (This bug has been fixed for
>     the next release, CR6350.)
> 
>     Mike
> 
> 
>     On 22 Jul 2004, at 9:05, Xu H.T wrote:
> 
>     >   Dear,
>     > 
>     >   I have check as the following two suggestion. However, the results seem
>     still >   unreasonable. For VAVsystems, it appears constant flowrate at
>     fixed supply >   temperature. Please help me to inspect this problem. > >  
>     The simulated system is very simple: mixed air flow through a cooling coil
>     and >   then suppied into room, using Hong Kong weather data file. I have
>     uploaded the >   folder: single room vav simulation > >   Thanks very much.
>     > >   Rgs, >   Xu >     ----- Original Message ----- >     From: Michael J.
>     Witte >     To: EnergyPlus_Support@xxxxxxxxxxxxxxx >     Sent: Monday, June
>     28, 2004 2:17 AM >     Subject: Re: [EnergyPlus_Support] one about vav
>     system > > >     This behavior indicates the coil is not large enough. 
>     Suggestions: > >     1.  Make sure the OA flow rate and the supply air
>     temperatures in teh ZONE >     SIZING and SYSTEM SIZING objects are
>     consistent with the simulation OA flow >     and temperature setpoints. > > 
>        2.  Use COIL:Water:DetailedFlatCooling, do not use
>     COIL:Water:SimpleCooling. > >     If this does not fix the problem, please
>     upload the input file to the files >     area in the Yahoo group or e-mail
>     zipped idf to energyplus-support@xxxxxxxx. > >     Mike > > >     On 24 Jun
>     2004, at 16:24, Xu H.T wrote: > >     >   Like the following email. >     >
>     >     >   I do a simulation for VAV system. The design day is used for
>     sizing of >     zone, >   system and plant. I set the supply air temperature
>     to 19C. I find >     with the >   design day simulation, the supply air
>     temperature isn't 19 >     (20.5 actually) and >   the air flowrate is
>     constant. However, for the run >     period simulation, the >   supply air
>     temperature is actually 19 and the >     supply air flowrate is also >  
>     constant. Why? Any suggestion for this >     problem. Thanks. > >   Xu > >  
>     ----- Original Message ----- >     From: >     zhaicq98 >     To:
>     EnergyPlus_Support@xxxxxxxxxxxxxxx >     Sent: Thursday, >     June 24, 2004
>     8:51 AM >     Subject: [EnergyPlus_Support] questions about dx >     vav
>     system > > >     I have two questions here. > >     First, I am >    
>     simulating a VAV system with no terminal reheat. I >     specify the supply
>     >     air temperature to be 12.8oC in cooling season and >     35oC in
>     heating >     season. According to results I got, it works well in >    
>     cooling season, >     trying to keep the indoor temperature under 23oC by > 
>        varing the supply >     air flow rate. While in winter, it keeps heating
>     >     the space to a high >     temperature. In heating season, the supply
>     air >     flow rate is always at >     its maximum value. I can not
>     understand why >     the supply air flow rate >     in heating season does
>     not vary. > >     Second question is about the >     iteration. I am using a
>     multispeed DX >     coil. The program terminates >     when simulating the
>     system in May. There >     is a fatal error which says >     the iteration
>     limit is exceeded when >     calculating the speed of the >     compressor.
>     I have no idea how to >     resolve the problem. > >     I have >    
>     uploaded the file named BOX4_VAV.idf to the files area. > >     Thanks. > > 
>        ----- Original Message ----- >     From: Michael J. Witte >     To:
>     EnergyPlus_Support@xxxxxxxxxxxxxxx >     Sent: Wednesday, July 21, 2004
>     11:09 PM >     Subject: Re: [EnergyPlus_Support] Glare index > > >     My
>     guess is that the coordinates or facing angle of the daylighting >    
>     reference point in these zones is incorrect.  Remember that daylighting >   
>      reference points are always relative to the zone origin, even when World > 
>        Coordinates have been specified.  In the dxf drawing file, the
>     daylighting >     reference points are drawn as a small red circle to help
>     you verify the >     location.  You may need to comment out all of the
>     daylighting objects and >     then add them back one by one to make sure
>     each reference point is within >     the appropriate zone.  If you are
>     unable to resolve this, please submit your >     input file. > >     Mike >
>     > > > >     On 8 Jul 2004, at 4:26, leeslwong wrote: > >     > Hi, >     > >
>         > I've simulated the daylight performance of a residential block which >
>     >     includes a kitchen, a living room, 2 bedrooms and a master bedroom. I
>     > >     called out the annual glare index with hourly basis of each rooms. >
>     The >     results show that there is no glare (means '0') in the kitchen, a
>     > bedroom >     and a living room. What situations would have these results?
>     > But there are >     glare index in other two rooms. Those five room have a
>     > window facing with >     the same direction (east). As I know glare index
>     > never reaches '0'. >     Anybody can tell me what's happening and how to >
>     solve it? > > Thanks > > >     lee > > > > > The primary EnergyPlus web site
>     is found at: > >     http://www.energyplus.gov > > The group web site is: >
>     >     http://groups.yahoo.com/group/EnergyPlus_Support/ > > Attachments are
>     not >     allowed -- please post any files to the appropriate folder > in
>     the Files >     area of the Support Web Site. > > Yahoo! Groups Links > > >
>     > > > > > > >     ======================================================== >
>         Michael J. Witte, GARD Analytics, Inc. >     EnergyPlus Testing and
>     Support      >     EnergyPlus-Support@xxxxxxxx > > > >     The primary
>     EnergyPlus web site is found at: >     http://www.energyplus.gov > >     The
>     group web site is: >     http://groups.yahoo.com/group/EnergyPlus_Support/ >
>     >     Attachments are not allowed -- please post any files to the
>     appropriate >     folder in the Files area of the Support Web Site. > > > > 
>              Yahoo! Groups Sponsor >                 ADVERTISEMENT > > > > > >
>     ----------------------------------------------------------------------------
>     >     Yahoo! Groups Links > >       a.. To visit your group on the web, go
>     to: >       http://groups.yahoo.com/group/EnergyPlus_Support/ > >       b..
>     To unsubscribe from this group, send an email to: >      
>     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx > >       c.. Your use of
>     Yahoo! Groups is subject to the Yahoo! Terms of Service. > > > > > [Non-text
>     portions of this message have been removed] > > > > > The primary EnergyPlus
>     web site is found at: > http://www.energyplus.gov > > The group web site is:
>     > http://groups.yahoo.com/group/EnergyPlus_Support/ > > Attachments are not
>     allowed -- please post any files to the appropriate folder > in the Files
>     area of the Support Web Site. > > Yahoo! Groups Links > > > > > > 
> 
> 
> 
>     ========================================================
>     Michael J. Witte, GARD Analytics, Inc.
>     EnergyPlus Testing and Support      
>     EnergyPlus-Support@xxxxxxxx
> 
> 
> 
>     The primary EnergyPlus web site is found at:
>     http://www.energyplus.gov
> 
>     The group web site is:
>     http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>     Attachments are not allowed -- please post any files to the appropriate
>     folder in the Files area of the Support Web Site.
> 
> 
> 
>           Yahoo! Groups Sponsor 
>                 ADVERTISEMENT
> 
> 
> 
> 
> 
> ----------------------------------------------------------------------------
>     Yahoo! Groups Links
> 
>       a.. To visit your group on the web, go to:
>       http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>       b.. To unsubscribe from this group, send an email to:
>       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
>       c.. Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/