[EnergyPlus_Support] Re: heat exchanger:Air to air: general
In addition, look at the E+ Engineering Document page 319 (page 346 of
413 in the pdf file) for an explanation of how Heat Exchanger:Air To
Air:Generic works with an air-side economizer.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "donbshireyiii"
<shirey@f...> wrote:
> Please upload your idf file to the EnergyPlus yahoogroups web site
> (http://groups.yahoo.com/group/EnergyPlus_Support/) or send it
> EnergyPlus-Support@g... and we'll take a quick look at it.
>
> If the temperature of the relief air is greater than the temperature
> of the incoming outdoor ventilation air, then you will see a
positive
> value.
>
> What weather file are you using?
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Joseph Lewis
> <fortierengineer@y...> wrote:
> > Hello,
> >
> > I have a heat exchanger:air to air:general in a model that only
> transfers sensible heat between the relief airflow and the outdoor
air
> flow. Running it in the summer design day, I have discovered that
no
> matter what control strategy for the out door air system, there are
> hours where the "Heat Exchanger Sensible Heating Rate" is positive.
I
> have looked at the HVACStandAloneERV_Economizer.idf example for
help,
> and it has the same issue. I have also looked at
DesiccantCVRh.idf
> and in this file the sensible heating rate is zero for the summer,
> but if I remove the desiccant unit from the loop you have the same
> issue.
> >
> > Is there a control strategy that can be used along with an outdoor
> air controller (with economizer) to eliminate this?
> >
> > Thank you,
> >
> > Joe Lewis
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/