The set points for economizer control in CONTROLLER:OUTSIDE AIR are set
at a maximum outdoor dry bulb temperature of 20C and a minimum outdoor
dry bulb temperature of 14C. This means that the HEAT EXCHANGER:AIR TO
AIR:GENERIC is only in economizer control when the outdoor air is
between these values. Notice the outdoor air dry bulb temperature is
above 20C during the morning hours of the summer design day. Since the
indoor temperature is 25C the heat exchanger heats the incoming outdoor
air. If you raise the maximum outdoor dry bulb temperature to 25.6C the
heat exchanger is in economizer during this time and the "Heat Exchanger
Sensible Heating Rate" goes to 0.0. The user is responsible for
determining the proper economizer set points for the particular climate
they wish to simulate. See Controller:Outside Air economizer
description and the description for Heat Exchanger: Air to Air:Generic
economizer mode for further details.
fortierengineer wrote:
> I have uploaded the file. It is called SHback to basics9-21.idf
>
> I am using the Pittsburgh TMY2 weather data.
>
> If it is of any help, currently the active control elements relating
> to the controller:outside air and the heat exchanger:air to air, are
> the set point manager:mixed air and the exchanger supply air outlet
> control (controlled by the "Seasonal Reset Exchanger Air Temp
> Sch").
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "donbshireyiii"
> <shirey@f...> wrote:
> > Please upload your idf file to the EnergyPlus yahoogroups web site
> > (http://groups.yahoo.com/group/EnergyPlus_Support/)
> <http://groups.yahoo.com/group/EnergyPlus_Support/%29> or send it
> > EnergyPlus-Support@g... and we'll take a quick look at it.
> >
> > If the temperature of the relief air is greater than the
> temperature
> > of the incoming outdoor ventilation air, then you will see a
> positive
> > value.
> >
> > What weather file are you using?
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Joseph Lewis
> > <fortierengineer@y...> wrote:
> > > Hello,
> > >
> > > I have a heat exchanger:air to air:general in a model that only
> > transfers sensible heat between the relief airflow and the outdoor
> air
> > flow. Running it in the summer design day, I have discovered that
> no
> > matter what control strategy for the out door air system, there are
> > hours where the "Heat Exchanger Sensible Heating Rate" is
> positive. I
> > have looked at the HVACStandAloneERV_Economizer.idf example for
> help,
> > and it has the same issue. I have also looked at
> DesiccantCVRh.idf
> > and in this file the sensible heating rate is zero for the summer,
> > but if I remove the desiccant unit from the loop you have the same
> > issue.
> > >
> > > Is there a control strategy that can be used along with an
> outdoor
> > air controller (with economizer) to eliminate this?
> > >
> > > Thank you,
> > >
> > > Joe Lewis
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
> ADVERTISEMENT
> <http://us.ard.yahoo.com/SIG=129ia167t/M=295196.4901138.6071305.3001176/D=groups/S=1705007389:HM/EXP=1095945490/A=2128215/R=0/SIG=10se96mf6/*http://companion.yahoo.com>
>
>
>
> ------------------------------------------------------------------------
> Yahoo! Groups Links
>
> * To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> * To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>
> * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> Service <http://docs.yahoo.com/info/terms/>.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/