Re: [EnergyPlus_Support] Purshased Air With Outlet Node problem
In PURCHASED AIR, "Zone Supply Air Node Name"=NODE_1 These node names should
match. In CONTROLLED ZONE EQUIP CONFIGURATION, "Zone Air Inlet
Node(s)"=Zone1Inlets. There is a NODE LIST named "Zona1Inlets" which maps to
NODE_1. The problem can be fixed by changing "Zone1Inlets" to "Zona1Inlets"
and the same for the other zones.
Mike
On 6 Oct 2004, at 13:58, leila wrote:
>
>
> Hi all,
>
> i´m simulating a building which doesn´t have any HAVAC system, but i
> need the values for purchased cooling rate and heating rate. But
> when i do the simulation the program abort with a fatal error and
> say that there aren´t any outlet nodes, can anyone tell me how to
> solve that.
>
> Thanks.
>
> Leila Félix Henriques ( Portuguese student)
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/