Re: [EnergyPlus_Support] A question about the all-outside-air system



The SYSTEM SIZING option will only impact the autosizing of coils in that 
system.  If you want 100% outside air in the simulation, you need an outside 
air system (with controller and mixing box).  In the CONTROLLER:OUTSIDE AIR 
object, set "MinimumLimit"="PROPORTIONAL MINIMUM" and set the "Minimum Outside 
Air Schedule Name" to a schedule which is 1.0 for the times at which you want 
100% outside air.

Mike


On 18 Oct 2004, at 14:54, huangyb@xxxxxxxx wrote:

> 
> I want to simulate an all-outside-air system in transition period. I find the
> items: Design Objects/SYSTEM SIZING/Cooling 100% Outside air and Heating 100%
> Outside air. Besides choosing "yes", I should do something else, I think. Please
> give me some advice. Thank you very much!
> 
> 
> 
> 
> 
> --http://www.eyou.com
> --Îȶ¨¿É¿¿µÄµç×ÓÐÅÏä  ÓïÒôÓʼþ  ÒÆ¶¯ÊéÇ©  ÈÕÀú·þÎñ  ÍøÂç´æ´¢...ÒÚÓÊδ¾¡
> 
> --http://vip.eyou.com
> --¿ì¿ìµÇ¼ÒÚÓÊVIPÐÅÏä  ×¢²áÄúÖÐÒâµÄÓû§Ãû
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/