Re: [EnergyPlus_Support] View Factors
Are there any internal gains (people, lights, etc.) that have a radiant
component? How are you reporting or inferring the amount of radiant exchange.
While it is true that the total radiant exchange should sum to zero, the
magnitude should change. Lower absorptances become a resistance to radiant
heat exachange. So, I would expect to see more heat flowing from warm to cool
surfaces when the absorptance is high, and less flow when the absorptance is
low. Is that consistent with the results you are getting?
Mike
On 21 Oct 2004, at 6:46, Peter G. Loutzenhiser wrote:
>
> I am modeling a small interior room with no windows--so no additional
> irradiation enters the space, and I have specified no thermal mass in the
> space. I look at the calculation method for radiation exchange and appears to
> be an energy balance between all the surface. I would expect from an energy
> balance that the heat transfer from some wall would be negative and some to be
> positive and, therefore, from a first law balance assuming steady-state
> conditions, the total heat exchange due to radiation would sum to zero.
> However, I have found that radiation exchange varies significantly (for this
> size of space) when I alter the thermal absorbtance. Perhaps I am misinformed
> and am completely missing an assumption or not factoring in additional elements
> used in the algorithm, but how can this be?
>
> Thanks in advance,
> Regards,
> Peter Loutzenhiser
> ISU
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/