This may be the result of a mismatch in the coil sizing inputs.  Make sure that 
the coil UA and water flow rate are consistent with the air loop flow rate and 
load.  

Note that COIL:Water:SimpleCooling will be eliminated in the next release of 
EnergyPlus, because there are some deficiencies in the model.  It is highly 
recommended that you use one of the other chilled water coil models, 
COIL:Water:DetailedFlatCooling or the new COIL:Water:Cooling.

Mike


On 21 Oct 2004, at 6:08, simon0176us wrote:

> 
> 
> My model with simple cooling coil always show following warning 
> message:
> 
> Convergence failure Simple cooling coil, iteration limit exceeded 
> 
> I tried the auto size and use the recommended UA value, but it didn't 
> help much. can anyone help me get rid off this message?
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/